Any supplementary bonding in place?
From what I see there wasn't any in bathroom but 10mm's to both water and gas and all pipes of boiler cross bonded with 6mm. Bathroom didn't have any extraneous parts could be touch simultaneously I.e rad and bath basinAny supplementary bonding in place?
Most shaver sockets are supplied from the lighting circuit which should be RCD protected to current regs and I believe C2 if serving a special location!
I could have used other equipment ITS NOT ABOUT A SHAVER SOCKET!
[automerge]1598032819[/automerge]
UNG its alright marking disagree but what do you disagree with?
1. Most shaver sockets are supplied from a lighting circuit!
2. The lighting circuit should be RCD protected!
3. It should be coded C2 in the instance of the OP's thread!
or
4. It IS about a shaver socket?
A very bad eBay special...What type of shaver sockets do you fit that RCD protection would make a difference
Ceiling height puts the downlights out of any bathroom zone. They are not in zone 2.t even though spots are not on rcd they are 2.25m above floor so fall within zone 2.
Just to play devils advocate here; if the property is for private rent then you could argue it's commercial and be more stringent on the coding (C2 lack of RCD on commercial whereas it may only attract a C3 on an home that is owned instead of rented - based on being more lax with electrical safety C's having the obligation on the PRS side of things. (You could FI and find out what limitations the LL places on the client (no drilling, no changing fixtures etc) as that could be a factor in your coding judgement