Any supplementary bonding in place?
From what I see there wasn't any in bathroom but 10mm's to both water and gas and all pipes of boiler cross bonded with 6mm. Bathroom didn't have any extraneous parts could be touch simultaneously I.e rad and bath basin

Most shaver sockets are supplied from the lighting circuit which should be RCD protected to current regs and I believe C2 if serving a special location!
I could have used other equipment ITS NOT ABOUT A SHAVER SOCKET!
[automerge]1598032819[/automerge]
UNG its alright marking disagree but what do you disagree with?

1. Most shaver sockets are supplied from a lighting circuit!
2. The lighting circuit should be RCD protected!
3. It should be coded C2 in the instance of the OP's thread!
or
4. It IS about a shaver socket?

In Napits Codebreakers a proposed C3 rating is given for 230v circuits supplying equipment in bathrooms or passing through zone 1 without RCD protection. I realise that is only a guide
 
C2 = 1 thing going wrong with turn into a C1 - How I've taken to looking at it, so would argue C2 for lack of RCD. Non fire rated Down lights in Flat with concrete barrier I would LIM simply because I couldn't verify the integrity of thr compartment formed by the concrete barrier
 
Just to play devils advocate here; if the property is for private rent then you could argue it's commercial and be more stringent on the coding (C2 lack of RCD on commercial whereas it may only attract a C3 on an home that is owned instead of rented - based on being more lax with electrical safety C's having the obligation on the PRS side of things. (You could FI and find out what limitations the LL places on the client (no drilling, no changing fixtures etc) as that could be a factor in your coding judgement
 
Just to play devils advocate here; if the property is for private rent then you could argue it's commercial and be more stringent on the coding (C2 lack of RCD on commercial whereas it may only attract a C3 on an home that is owned instead of rented - based on being more lax with electrical safety C's having the obligation on the PRS side of things. (You could FI and find out what limitations the LL places on the client (no drilling, no changing fixtures etc) as that could be a factor in your coding judgement

Doesn't matter what limitations are in the contract, the tenant will still put a shelf up if he needs one unfortunately.
 