The consumer unit was only installed last year to 17th edition Amd 3 & now the customer wants a SPD fitted after a friends £2k TV got fried by a lightning strike.
As MK do not make SPD, can you fit another brand of SPD in the consumer unit.
I know the rule about mixing brands of MCB/RCBO in a consumer unit, but does this apply to a SPD.
I believe the rule you talk of applies to all CUs and associated equipment, unless you have manufactures assurances that to mix and in the particular instance is OK, why not fit a Type 1 SPD at the origin of the installation 534.1 table 3.7.3 OSG Page 41
Unfortunately there is no space to fit a separate SPD, as it's all in a cupboard with the meter above the front door.
A type 1 SPD is for installations with an LPS
A type 2 would be more appropriate
The reason I opted for a type one was because the OP was questioning the use of mixed units in the CU , and an upfront SPD may be the answer, looking again though your choice has it's merits a good call on your part.
Got a reply from MK.
Although they do not make a SPD they have approved one by Phoenix Contact, but can only find it at RS at the cost of £283.82.
Only four times the price of a fully loaded board in Screwfix.
  • Sentry Surge Protection 18th Ed Tech 2019.pdf
Reply to Fitting a SPD to MK Consumer unit in the UK Electrical Forum area at ElectriciansForums.net
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...