The correct method for calculating the protective device is as follows.
30 x 58 x 1.8 = 3132 W
3132 Divide be 230V = 13.61A
The protective device should be 16A
The normal type this type or lighting should be type C.
Cable calculations should be based on a load of 13.61A
Doesn't always work, mate. You can easily run out of ZS using cables rated for 13a e.g. 1.5. Its nearly always ZS i am chasing not load or volt drop when using C and D type breakers.
Worst case scenario is when the Db is at one end and the switch is at the other end