is it ok to wire a heating system with .75 flex as it is protected by a three amp fuse all answers welcome
 
S/L is looped in the boiler for a combi / loop removed for system boiler(insert sw-wire in S/L)

I really think you're confusing some people here with your replys as they aren't overly clear. Normally when wiring a combi you will have a supply to the boiler (permanent live, neutral and earth). To satisfy Part L of Building Regs you would normally wire a 4 core flex (or 5 core if the on signal is volt free) to a room thermostat of your choosing. Isolation for mechanical maintenance would then be via the FCU which is located beside the boiler.

When wiring a S or Y Plan the main supply for the central heating system would often be located in the airing cupboard (beside the cylinder) as this is often the easiest and most efficient (from a cabling point of view) place to locate it. You will then (normally) require 4 or 5 cores sent to the boiler from the main wiring centre which would normally be located elsewhere in the property. The 4 cores will cover you for permanent live, switch live (on signal to boiler), neutral, earth and in some instances a 5th core is required to operate the pump (where the boiler has a pump overrun fitted). Due to the boiler being located remote from the point of isolation a isolator for mechanical maintenance is required. This would normally be a 3 pole isolator which would isolate PL, SL and N. In the instances where a pump overrun exists the core feeding the pump obviously does not need a switch in line with it as isolating the PL and SL supply to the boiler will automatically de energise the pump if the system is wired correctly.

There are however some exceptions which mostly exist in electric, oil fired boilers and old gas boilers. Often oil fired and old gas fired boilers will only require 3 cores (SL,N+E) as the boiler doesn't have a flue fan or pump overrun facility. Also, electric boilers will often have volt free switching so an additional core (6 cores) will be required. There are still more exceptions to the above but i hope i've covered most bases and everything makes sense.
 
Also, as a side note, the isolator beside the boiler is a requirement of the plumbing regulations as far as i know. Don't think there is a specific electrical regulation that states that isolation is required at the boiler itself however it is good practice unless the isolator in the airing cupboard is lockable. I stand to be proved wrong but that is my opinion without getting the BRB out and spending hours flicking through it which i'm not about to do on a Sunday! :rolleyes:
 
what makes sense to me is to fit the isolator next to the boiler. i was always taught to fit isolators within reach of whatever they fed. e.g. cooker switch within 2m of cooker. i would never fit a cooker switch in an airing cupboard so would not do it for a boiler unless that was the location of the boiler.
 
what makes sense to me is to fit the isolator next to the boiler. i was always taught to fit isolators within reach of whatever they fed. e.g. cooker switch within 2m of cooker. i would never fit a cooker switch in an airing cupboard so would not do it for a boiler unless that was the location of the boiler.

So what about the motorised valves, pump and other controls? If you were working on them then the isolator would not be 'within reach' if it were just at the boiler. Horses for courses i suppose but i've always wired it as i've explained above as it saves on having two wiring centres when you consider how many cores a modern boiler can require.
 
There is nothing in the regs regarding the position of the isolation, but if it is placed remotely then as per reg 537.2.1.5 it must be able to be secured in an open position either by lock or removal of handle. As a normal domestic FCU will not give you this then it is always considered to be best fitted locally.

As for the Isolation part a double pole isolation as a FCU would give, for the main supply into the boiler would give you adherence to regulation 537.2.1.1 for a TT system and if it was a TN system then a single pole device would be more than adequate.

As this would kill the boiler circuit including any control circuits, I can't see why you would want to also isolate a S/L
 
As this would kill the boiler circuit including any control circuits, I can't see why you would want to also isolate a S/L

But in the instance where the boiler is wired to a S or Y plan where the main supply (a non lockable FCU) is located in the airing cupboard then 3 pole isolation is required at the boiler as the SL in to the boiler will still be energised. Is this making sense?
 
As Dunc so rightly said. Take this scenario!---Boiler fitted on wall to nearest GAS/WATER supply (say outhouse) no electrics in sight(convenient for gas fitter) all controls ie: valve/cylinder stat/pump fitted in cylinder cupboard.Room stat self explanatory,hard wired or wireless.
Logical power supply located------------------You guest it IMMERSION HEATER SUPPLY,now for the dreaded 3pole isolator fitted at the side of the boiler,to isolate 1/switch wire 2/permanent feed 3/neutral.
WHY PERMANENT SUPPLY????? I Hear you scream, most modern boilers have digital displays or self diagnostics and require it. Just to hop back a post or two, 7core 0.75 from cyll cupboard to boiler you can now fit the controller at the side of boiler hence 4core from controller to 3pole isolator to boiler.
PS. Look for isolation for maintainence !
 
Last edited by a moderator:
afraid this discussion is now going way above my head as my knowledge of heating systems is confined to chucking another log on the wood burning stove.
 
I have my boiler in the garage and the motrized valve and the pump is in my airing cupboard. Are you saying that you would not still fit a 3 pole switch on it if you made the FCU safe, by removing the fuse in a domestic situation.?
 
I have my boiler in the garage and the motrized valve and the pump is in my airing cupboard. Are you saying that you would not still fit a 3 pole switch on it if you made the FCU safe, by removing the fuse in a domestic situation.?

But removing a fuse from a FCU is not locking it off. I'm probably being pedantic here but there is nothing to stop someone bunging a fuse back in it and switching it on while someone is working on the boiler. Like i said a few posts back the isolation switch at the boiler is a requirement of the heating regs similar to how a boiler in a loft must have adequate lighting and access which includes solid floors leading to and around the boiler. If nothing else there is often a section in the boiler's installation manual that states that isolation must be present at the boiler itself. We therefore have to apply to this rule as there is a reg that states that equipment must be installed as per the manufacturers instructions.
 
Thanks Dunc this is what started it off really. I agree that technically someone could but a 3amp fuse in a boiler FCU in a garage while you were upstairs in the airing cupboard, though unlikely, technically it is possible, the same as someone might have a spare handle to an isolator on a commercial/industrial site.

As I asked originally is this 3 pole isolator not only a part of the heating regs, which I will honestly say I have little knowledge of, but also in most manufacters instructions?

Taking this further what would the situation be if at the boiler in the garage rather than having a FCU that can not be locked. you actually fitted a lockable isolator?, would in your opinion stll need this internal 3 pole isolation for the S/L, L and N if on a TT
 
Taking this further what would the situation be if at the boiler in the garage rather than having a FCU that can not be locked. you actually fitted a lockable isolator?, would in your opinion stll need this internal 3 pole isolation for the S/L, L and N if on a TT

I would say the lockable isolator would satisfy our regs but the heating engineer would be having a right go at you. Ruddy plumbers! :rolleyes: To be honest even if it wasn't for the other trades regs i would still fit an isolator beside the boiler as a matter of course in the interests of good practice.
 
All very interseting reading.
I am currently re-wiring a flat- not being a member of a scam club yet I'm doing this through the local authority's building control. The new owner of the flat is also having a new boiler fitted but a GasSafe registered plumber is doing that. The original boiler was simply plugged into an adjacent switched socket outlet in the kitchen. British Gas initially quoted to replace the boiler and they insisted that a switched spur box was fitted as supplying the boiler from a socket outlet is no longer allowed "under the regs". Sounds reasonable to me. In order to get a better quote than the "arm and a leg" that British Gas wanted the owner has had three GasSafe registered plumbers to quote for the job and all three have said that it is perfectly ok to feed the boiler from a switched socket.

Like everyone else on this thread I have trawled through BS7671 and failed to find any regs regarding the electrical supply to a boiler. But British Gas are a professional outfit so if they say it is required then I'm inclined to think that is true.

Two questions I have are:

1. Is it ok to supply the boiler from a switched socket outlet or does it have to be done via a suitably labelled single/double pole switch and fuse situated adjacent to the boiler?
2. Is it ok to supply it from the radial final circuit to the kitchen or does it require a dedicated feed from the cu?

I could just do what the plumber is happy with but if the local authority's inspector fails it when he makes his inspection I'll only have to do it again.

Thanks in advance.

mia
 
As the discussion went on here for the BS 7671-2008 a boiler can be feed from a BS 1363 socket and plug.

As Dunc tells us the gas regs are a different entity in themselves by the looks of things
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
heating question
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
33
Unsolved
--

Advert

Thread statistics

Created
vinny electric,
Last reply from
malcolmsanford,
Replies
33
Views
5,305

Advert