From what I remember if the links in the motor terminal box are in a straight line across three terminals its star...if the links are arcoss two terminals each link its delta.
Running in delta will get the max out of the motor.
That is Star
Delta there will 3 links
 
Last edited by a moderator:
Thanks for everyones help on this.

Just one last question. if one of the windings had failed could this cause the motor to run slower ( if it was running on 2 phases instead of 3) or would it not run.

Also i have noticed that the last electrician has swapped the yellow and red phase over in the bottom of the contactor. would this cause the fan to run slower.

I am back out there on monday trying to sort things.

i will try and swap the windings from star to delta first

then if nessarcery i will wire it as star/delta.

The fan has taken out the overload after around 20mins of running a couple of times. the overload is set at 5A at the moment so i have incresed this slightly. what could cause this.

alos the fan that it is running is around 2.5foot wide

If you lost a winding and as long as it was not shorting to earth then that could make the fan run slower. Easy to check just test all 3 windings and see what values you get.

Swaping over the phase will just change the direction of the motor it will not affect the speed it runs at.

If the motor is not runing at full speed ie "labouring" then it will increase the amps, like a water pump if you over design it's capacity ie you need to deliver 50 litres per minute but fit a pump that will deliver 500 litres a minute it will trip out on over load.
 
Hi

no need to run the motor in star delta, check the current the motor pulls on each phase, the o/load unit for the motor would trip with an out of balance load and the motor would get hot if the motor was two phasing.
if the fan needs to go faster have a look at an invertor
 
To be brutally honest I really don’t think you’re competent to carry out this work! I don’t think you have the basic concept of a 3 phase motor.
Sorry
 
No motors arent what i specialise in. I specialise in stage lighting and testing. the last time i dealt with motors was 14 years ago at college. That is why i have asked for the help and support of people who do. If everyone did the same then maybe we wouldnt have so many bodge jobs out there.
 
Capable of doing the job or not is your decision at the end of the day. To me it sounds like you know enough to work safely so if the job is outside your skill set it could just work out expensive if you damage the motor.

Whatever you decide to do with the installation as long as the motor is running within it's specified run current on the info plate and as long as the current draw on all 3 phases is within 5% of each other then you shouldn't cause any damage further to what might have already been done.
 
Firstly, a 5.5kw motor on 3ph 400v will draw approx 11 amps FLC so the overload, at 5 amps is undersized. Ensure your overload can be set to 11 amps.

The motor, according to the nameplate, should only be connected in either star Y

StarConnection.jpg


or delta

DeltaConnection.jpg



If it's a dual voltage motor then it'll be 400v Y, if a bog-standard 3ph motor more likely delta but confirm that with motor plate. If you connect it incorrectly you'll soon smoke the motor.
I'm sure you do understand that the connection has no real-life function as a speed control. If that motor is a 1500rpm motor then changing from star to delta will not change the speed for use.

Of course, you can use star-delta as a starting method only, not a speed control. The 'slow' speed in star-delta is the reduced torque building up to overcome the inertia of the load.

To reiterate the two-speed motor possibility (albeit unlikely) this utilises the star and delta connections to alter the usage and connections of the windings... but lets forget this option now.

Finally as one of the posters mentioned... bell the motor windings out then ensure you are getting full voltage through the DOL to the motor. Good luck. Please let us know what you find.

.
 
I have belled the windings out and they all came out equal at 4.6 ohms. The motor is currently wired in delta. I think the customer has given me so duff information which has confused things.

I was told that it used to run faster until the last electrician came in

They forgot to mention that.

The motor has been removed and rewound since then

also the fan unit is supposed to be cleaned regulary but this has not been carried out.

Could the problems with speed be that the load is to much for the motor.

The belts are to tight

maybe it was rewound differently to the original.

These are all things that would of been nice to know a little earlier

If the motor is daul voltage how would this be marked on the plate?

thanks
 
If a dual voltage motor the plate would be similar to;

img_0137.jpg


220-240/380-415v Y/D... so 220-240v ie. off a 1ph inverter would be connected in delta else 380-415v in star. 4.5 amps in delta. 2.6 amps in star.

.
 

Reply to Help with a 3 phase star delta motor in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
819
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
352
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock