Hi everyone,

Just having new kicthen installed and noticed that they wired 2.5mm HR flex off the cooker switch. The 2.5mm HR flex feeds to a dual cooker outlet which will power a 16amp cooker and a 32amp induction hob. The cooker switch is 6mm cable with a 32amp breaker.

Is this okay?

Many Thanks
 
Who's wired it up and has there been any other electrical work / alterations done?

A Kitchen Fitter?
An "Electrician"?
Or a Trained and Qualified Electrician, who will issue paperwork for the electrical installation?
 
Thanks for your reply so it's not wired correctly as from the cooker switch to the dual outlet is 2.5mm HR flex but from the fuse board to the cooker switch is 6mm t+e.

It doesn't sound like it's wired correctly - The cable from the cooker switch to the dual outlet plate should be equivalent rating to the cable back to the fusebox. to allow for the loading that might be placed on it now or in the future.

Check that it is 2.5mm flex as it's just possible that it's wired in 4mm Flex, which would probably be OK since that can have a rating of 32A. However, if this is a kitchen fitter installing then that seems unlikely, as 4mm flex is less common and can't be obtained as easily from the likes of Screwfix.

From the Dual Outlet Plate it is reasonable to wire in 2.5mm HR flex for the oven and then a suitable flex to the hob (4mm may well be the right choice for that, though many hobs come with their own flex which is sometimes smaller because the manufacturer has decided that is safe)
 
Just to add that you should be getting a certificate for this work, And that means someone actually testing it to ensure that the earth continuity is complete, etc, RCD protection is in place for the new sockets, etc.

If the person installing doesn't have the facility to test that, then he shouldn't be doing the work.
 
Thanks for everyones replies, The fitter told me because its an existing circuit the work isn't notifiable so he can carry it out. So if he wires from the cooker switch in 6mm t+e to the dual outlet and then 2.5mm HR to the oven and hob this will be okay?

Or probably best to get an electrician to inspect the whole circuit?

Many Thanks
 
Get an electrician in full stop never let a kitchen fitter touch your electrics.
An electrician should provide you with a Minor Works Certificate, a kitchen fitter will provide you with nothing as they know no better.
 

Reply to Help! With oven and hob wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
659
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
879
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
886

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock