Ok just a quick question to confirm my suspitions.

A 4mm radial in metal containment for sockets is ok as high integrity earthing as both the 4mm CPC as well as the metal work are classed as eaarthing conductors so there is a parallel earth path.

Please correct me if i am wrong
 
Depends if the equipment being fed from this radial circuit requires an isolated (so-called ''Clean Earth'') earth or not? This subject has been covered in quite a few threads now, which can be seen at the bottom of this page under ''Similar Threads'' ...why not have a read.
 
A 4mm radial CPC within any form of mechanical protection is fine confirmed in this link http://electrical.------.org/wiring-matters/26/5437-earthing.cfm?type=pdf
 
4mm single core rings in steel trunking supplying twin sockets with seperate earth terminals and CPCs seperated at main earth bar.
testers a muppet and has seen PCs and put it as a fault without looking.
 
e54 if the cable was 4mm singles in dado trunking or 4mm t&e using high integ sockets and the cpcs in seperate places in earth bar back at board would we need to run a seperate earth as well or would it be acceptable
 
e54 if the cable was 4mm singles in dado trunking or 4mm t&e using high integ sockets and the cpcs in seperate places in earth bar back at board would we need to run a seperate earth as well or would it be acceptable

If were talking about an all 4mm ring circuit or radial supplying a load with ''over'' 3.5 mA, 4mm CPC's on a ring or radial circuit would be acceptable, as dado trunking and PVC conduit etc, i would think is a suitable mechanical protection. 4mm T&E only has a 1.5 CPC conductor and would i think, not comply..

Best person to ask for a definitive answer is Malcolm, who is well versed in IT installations. I'm used to providing steel conduit/trunking containment installations in this area, with higher than minimum provisions...
 

Reply to High integrity earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
516
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
610
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock