Discuss How do I calculate the resistance of a spur without phisically testing ? .. in the UK Electrical Forum area at ElectriciansForums.net
Boffins of the electrical world ... How can I calculate the resistance of 48m ring 2.5/1.5 .. with a 8m spur .. I can quiet easily do this without a spur in the equation but , my test papers require my doing so with an 8m spur. . how does this affect the zs tests ... Thanks v much ...
If I were doing that question,
I would first work out the values for the furthest point of the ring, 24m with equal cable lengths of the ring back to supply. (worst case scenario)
assume the spur is taken from that point.
then calculate the values for the spur itself (8m)
resistances in series are simply, added together to find the total resistance.
have a go at it with the above mentioned in mind.
Hi - if I’ve understood correctly - calculate the spur component as if it was an 8m radial of 2.5/1.5 and add that value to the ring plus Ze.
It doesn't say whereabouts on the ring the spur is connected. If you were simply asked to prove compliance, then provided it complies under the worst-case conditions you can answer that. But they do ask for a value for Zs (which may be highest at the spur) which IMHO makes it a daft question.
R1+R2 for the ring should be an easy calculation from the end to end values you have already worked out.
Then add the R1+R2 for 8m of cable to get the R1+R2 at the end of the spur, the location of the spur on the ring doesn't make a difference to this.
Without further information I would give the Zs of the ring and the Zs at the end of the spur assuming it is connected at the mid point.
From memory table I1 in onsite guide “I think” gives you the resistance values in milli ohms per meter of various size conductors.
once you have that multiply it by length of spur decided by 1000 to give the resistance of spur. Add that to the ring resistance, done.
As others have said not enough info on where the spur is taken from the ring
Reply to How do I calculate the resistance of a spur without phisically testing ? .. in the UK Electrical Forum area at ElectriciansForums.net
I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options. Continuity of a ring...
So I'm starting out a new rig and I'm fresh out of college with my level 3 without any experience and I think that I need to still have the...
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
7K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...