tommys88

Basically yesterday I upgraded a fuseboard as the previous had no RCD protection so I installed a 17th edition split board.
Basically got board in, then one of the rcds would not set in with NONE of the breakers even switched on?! So i removed all the cables out of the neutral bar putting back one at a time to establish what was holding in etc established it was a problem with the kitchen ring!
Basically whenever the neutral and earth are connected in the board rcd won't set so if the earths are not connect ad neutrals are rcd holds vice versa! Does this mean there is an earth neutral fault somewhere on the ring?and is so what's the best way too find it? :confused:
 
Pretty much, could be either earth->neutral or line->neutral though. Make sure all of the appliances are disconnected in the kitchen and retry. If it still trips immediately then visual inspection of all the sockets again and look very carefully for small nicks etc in the inner core insulation.
 
first of all, i wopuld split thering, and start testibg from there, IR test between conductors. when youve found theside of the ring with the problem, then split that side in 2, until you find the problem. when found, do a full set of tests to ensure no cross connnected rings ect.


testing should be carried out on an installation before a board change, to ensure that this doesnt happen!
 
Yeah I should of said I took all the sockets off no nicks or anything like that visible unfortunately! How do I establish which fault it is line-neutral line-earth or neutral-earth fault? Then best way is just to split it in the middle and trace each leg is that right?
 
Un plug everything on the ring final, and if there are FCU on them then turn these off, then at 250v do a L/N-E IR test and see what you get.

If you get a low IR reading and you have made sure everything is disconnected then break the ring somewhere in the middle. Then do another IR test on both legs, this will then narrow it down further and you just keep on doing this
 
Yeah I should of said I took all the sockets off no nicks or anything like that visible unfortunately! How do I establish which fault it is line-neutral line-earth or neutral-earth fault? Then best way is just to split it in the middle and trace each leg is that right?

You do it with insulation resistance tests as you would on a newly installed circuit.

Have you done any testing at all on this work?
 
Yeah I should of said I took all the sockets off no nicks or anything like that visible unfortunately! How do I establish which fault it is line-neutral line-earth or neutral-earth fault? Then best way is just to split it in the middle and trace each leg is that right?

No,the fault will still be in circuit
 
Yeah I'm an electrician only been qualified a year, it's thorugh my own naievty I don't usually do private work but as I favour I said I would upgrade there board for them as a favour thinking straight swap teat after lovely..... But obviously bit and um learning from my mistakes now!
 
Yeah I'm an electrician only been qualified a year, it's thorugh my own naievty I don't usually do private work but as I favour I said I would upgrade there board for them as a favour thinking straight swap teat after lovely..... But obviously bit and um learning from my mistakes now!
what test instruments do you have / are you using?
 
Then start from scratch as you'll have the correct equipment. Visual inspection first, end-end continuity of conductors, ring continuity tests. BEFORE you do any IR testing please.
 
Yeah I'm an electrician only been qualified a year, it's thorugh my own naievty I don't usually do private work but as I favour I said I would upgrade there board for them as a favour thinking straight swap teat after lovely..... But obviously bit and um learning from my mistakes now!

You can't take a consumer unit change lightly, more fires start in the consumer unit than anywhere else, testing is very important!

Then you need to issue an Electrical Installation Certificate and notify the work to Building Control under Document P regulations.
 
Yeah I know I understand this now but I want too rectify it so I'm trying too do what's right and follow advice on here! Iv done all the continuity tests and earth loops are all fine! Ir is coming up 0.00 iv got a megger multiple functional tester! I'm pretty sure iv unplugged everything but there is a lot of units which could be concealing power points?
 
Also lucky enough they are putting in a new kitchen as they have just moved in so if worst comes to worst I can install a new kitchen ring without major dramas!
 
So you think you may be doing the ir test with equipment still attached? Really need to sort that before you do ir, just hope you've not damaged anything.
You know a kitchen ring is notifiable also?
 
If you seperate the kitchen ring into small sections then IR each section, you will quickly locate the fault, then if need be, just renew the faulty section.
 
your first step is to ensure all appliances are unplugged ( not just switched off ). then, if the fault is still there, split ring as said before and IR test each half. then split the faulty half in half again. quite possible to find a JB plastered in, nail through cable, short circuit to metal back box, and a few more i could mention when i've woke up properly.
 

Reply to How do I go about detecting this fault..... in the Australia area at ElectriciansForums.net

Similar Threads

Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi Basically I have visited a youtube link of another electrician and he is talking about how many electricians find RCD fault very hard to...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock