Has anyone had any issues with Sunny Boy inverters before? We've had one playing up on us for the last couple of weeks. On a couple of occassions now, we have had "Disturbance" come up on the inverter. I haven't been there to witness it so can't give any more information. The inverter has shut down for an hour at a time while this is happening.

Could this be something from the grid?
 
I'm visiting site on Saturday morning. Earliest I can get there. I need to speak to SMA technical, really, but it would be pointless unless I was stood in front of the inverter. Hoped that someone else may have come across a similar problem and could suggest a solution. If it's something to do with the DNO then I know I'm in for a nightmare.
 
Has anyone had any issues with Sunny Boy inverters before? We've had one playing up on us for the last couple of weeks. On a couple of occassions now, we have had "Disturbance" come up on the inverter. I haven't been there to witness it so can't give any more information. The inverter has shut down for an hour at a time while this is happening.

Could this be something from the grid?

I've just looked in the manual and found this

DISTURBANCE This error is generated for safety reasons and prevents the Sunnyboy from connecting to the grid

Corrective measures contact SMA Solar Technology Serviceline

you'll have to phone them I found them to be very good they rang back straightaway (+49 561 9522 1499) or email ([email protected])
 
I had a problem on Monday, customer who's system was installed last week called to ask why his inverter had inexplicably shut down for 2 hours during the day on Saturday. The inverter is an SB3000HF

I called SMA support in Germany and had a long chat with a very knowledgeable and friendly engineer. He reckoned that grid problems were most likely to have triggered an under/over voltage/frequency shutdown. The inverter knows why it shut down but only an SMA engineer can access that, everyone else needs to witness the error code at the time of the shutdown.

We discussed options for troubleshooting and the common solution used in Germany is that installation engineers have their own bluetooth webbox and leave it on a customer site for the first couple of weeks. The installer then can monitor the system and has a record of any error messages. They then call back and collect the box and perhaps sell them one as well.

I asked for an SB4000HF to deal with larger systems without needing to to TL and for the sunny explorer to be able to email error codes to the installer. I was asked to put my requests for product development into an email which I did.

We left it that the customer would monitor the system (with their Sunny Beam) they can easily see any shutdown periods on the display. If the problem re-occurs then I will buy a webbox and monitor the error codes remotely.

Hope that helps.
 
Thanks for the info, fellas. If things go well today then I should be able to get there this afternoon and give SMA a ring. I will let you know what the outcome is - if there is one.
 
Managed to get out there this afternoon and it looks like it might be a grid problem.

We measured a voltage of 258v (although we measured 247v when we tested originally) and we think this may be why the inverter is kicking out. If the voltage is fluctuating then there is a good chance it's going above 260v and therefore beyond the tolerance of the inverter. I rang the DNO this afternoon and they are going out to look out at on Monday morning.
 
I am having a bit of an issue with a 3000tl at the moment- grid disturbance code 4- which is "Check the power supply line for strong, short-term frequency variations."
Anybody else ever had frequency issues? Had a few issues with grid disturbance faults on the TL's such which has led to upgrading of cables on a job I was commisioning as a subbie- 3.92kwp on a 2.5mm and another one which ended up with a new earth rod. Never had frequency though. I thought frequency was pretty stable in most places
 
The only issue we have had with an install was with a Sunnyboy TL3000 which would inexplicably shut down for anything from 20 minutes to an hour, it turned out that the two rotary switches inside the control panel were set to '0/0', which is the standard German setting, instead of '5/8' which is the UK setting. This caused the inverter to shut down whenever the grid voltage went above 250v according to the very helpful German engineer we spoke to.
 
The only issue we have had with an install was with a Sunnyboy TL3000 which would inexplicably shut down for anything from 20 minutes to an hour, it turned out that the two rotary switches inside the control panel were set to '0/0', which is the standard German setting, instead of '5/8' which is the UK setting. This caused the inverter to shut down whenever the grid voltage went above 250v according to the very helpful German engineer we spoke to.

Bloody hell, This is gonna make me sound a bit stupid now but I thought they were just for the sunny display address.
 
The SunnyBeam / Sunny Explorer is usually just the 'C' dial.
 
BiggsSolar, get the client to check site volts (with cheapo plug-in power meter) to see if this is the problem? This is the only problem I have ever had (except German set inverters )
 
I just wanted to say thanks to the contributors to this thread as it has helped me with my system. I had a Sunny Boy 4000TL installed in early November and suffered about 2 outages per day due to "grid disturbance", with the inverter cutting out for about 11 minutes each time whilst it checked the grid voltage. By switching off and on again (on the AC) side I was able to get the start up message indicating German voltage settings ( I got ADJ rather than G83/1).

I also monitored the grid voltage which at that time was about 245-250 volts (it has since dropped to about 240-245 and I am close to my substation). As the G83/1 upper limit is 253 volts (230 + 10%), I was fairly sure that the inverter was set wrongly. After sum digging, I found that the inverter had been imported to the UK set to German voltages (which I guess must be about 250 max), but the importer assumed it was set to UK voltages as did the installer. SMA claim that the voltage setting should have been on a label on the box, but neither I nor the installer saw it. Unfortunately, after about 12 hours, the inverter protects itself from adjustment so that the country voltage settings cannot be reset using the mechanical dials (these should be 5 and 8 for the UK and were 0 and 0: the default). I have finally got the installers back who spent about 2 hours resetting it to G83/1 via security code (from SMA who were very helpful) and blue-tooth to the inverter. If only SMA had put a label on the inverter itself stating the factory setting, or the importer had done the same, or the installer had checked the setting and reset via the dials .... life would have been a lot simpler: but hey, I have learned a lot about the Sunny Boy, the European grid settings etc. The voltage limits are now 100-207 minimum and 264-280 maximum which should be fine.

I hope this helps others with the same issue.
Regards
Vaughan
 
I find it disturbing that installers are installing SMA inverters without reading the installation manual. It is quite clear that the correct country standard and language setting should be checked before commissioning.
My teams are all trained to check this both physically when installing the inverter and on commissioning when the display first comes to life. It should state that it is set to English language and then G83/1.
 
Hi All

My 4000TL keeps cutting out with a grid disturbance every few days and the red fault light comes on.

When that happens, it does not reset but stays off and gives no output, sometimes all day.

I think the installers set it to GB settings because we checked it at the time of installation and it was in German or something (it does say English now) but I did notice that it also says C10/11.

I didn't notice it saying G83/1 so is it maybe set wrongly?

My Sunnybeam registers grid disturbances once or twice every day but it only cuts the inverter out evry few days.

I have emailed SMA support (thanks for the contact info further up the thread) but do you guys have any suggestions?

Cheers

Dave
 
I believe C10/11 is Belgium's settings. SMA inverters can be set to any country's setting yet be forced into English language. Sounds to me that this is what is happening.
 
Your installer will need to get the code. You won't be able to get one yourself as the end user.

Hi

The system was installed via my own company. My company purchased all the kit and the installers fitted it. I subcontracted the installers so effectively, I am the supplier/installer.

I take it I will definately need a code to change it?

Cheers

Dave
 
Yeah, if you've had the inverter operating for a while. You need to speak to SMA about applying for a Gridguard code. Takes a couple of days.

Then you'll need a laptop with bluetooth.
 
Yeah, if you've had the inverter operating for a while. You need to speak to SMA about applying for a Gridguard code. Takes a couple of days.

Then you'll need a laptop with bluetooth.

Hi

I emailed SMA and got GridGuard Code application form - filled it in and got the code yesterday. I got the inverter sorted today.

The email stated to use Sunny Data Control software but I couldn't get it to see/use the bluetooth adapter.

I then used the Sunny Explorer software and that worked fine. If I remember correctly, I clicked on Tools and selected GridGuard and that let me put the unlock code in. After a few seconds, the inverter clicked a bit then the green generating light went off.

After that, I clicked on the Settings tab, clicked the down arrow on the gridguard section and then clicked the edit button. Went to the country code bit and changed to G83/1 - It took the setting ok and a few minutes later the generating light came back on and all seems to be fine now.

Hopefully this bit of info may help somebody out.

Cheers Guys

Dave
 
Yeh i had this grid disturbance problem.Connected to sunny explorer entered grid guard code and changed the country settings to g83/1.
I think this is a very common problem and most pv installers especially when starting out after passing there mcs had to go back and change country settings on sma tl inverters due to incorrect 1st time commissioning.
Happy days were all still learning.
 
SOLUTION(Mine) - Sunnyboy 3800 Voltage Disturbances Vac-Srr - 263.9V present, 259.1V now. Should be 216-253 (230)V-6%+10%.
PV system trying to deliver 3.6 kWh.
Voltage at generation meter shows 257-260V.
Solution:-
1 - contacted SMA uk via online form with Serial no. also mentioned that Inverter in loft with 15m of 4mm twin and earth.
Reply from SMA :-
a - inverter set to UK settings at factory.
b - 4+4mm cable may be light (my calculations suggest 2.5V drop over 15m at peak current.
c - suggested I speak to distributer as voltage high on mains.

2 - Contacted Electricity North West at 4:30pm - Emma took notes.
Reported high voltage especially at mid day on sunny days.
a - asked if I was available until 8pm?!
...me - it's not that urgent?!
b - 8:15pm Pete arrived. Saw my readings agreed accurate as inverter similar.
c - Pete checked mains before mains meter. 253.7V.
d - powered down our PC'S etc. Power off and line impedance checked ok. Power up again.
e - Pete agreed Voltage high/too near max and would visit substation 200m away.
F - Village blacked out for 5 mins at 11:05pm. (Not my fault honest!) Possibly moved transformer to next tapping.
...
Me - 8am checked mains supply at generation meter... 243V when generating 1kW. Probably no need to upgrade the cable from the inverter just yet.
Well done Pete and Emma from enw.

Hope this helps someone else.
Thanks to the forum for pointing me in the right direction too.
Nev
 
Just
I find it disturbing that installers are installing SMA inverters without reading the installation manual. It is quite clear that the correct country standard and language setting should be checked before commissioning.
My teams are all trained to check this both physically when installing the inverter and on commissioning when the display first comes to life. It should state that it is set to English language and then G83/1.
just about to say same thing from the above posts it is clearly stated in the install instructions set country of origin codes
 
Hi all - new to the forum.
Retired Contractor in HVAC, Electrical, General.
I have 3 Sunny Boy Inverters in use, 2 of the 3000TL-US, and a 6000TL-US.
All of them show 127V-130V output on the display, despite being 220VAC.
An amp-draw shows correct amperage at 220VAC.
So now I'm perplexed - why does the display show one leg ?
 
You're probably reading the DC input....

Photos of the displays would help
 
Your original post at 2:20 am UK time (BST) suggests you were up late or that your location is correct e.g. California and your time was 6 or 7pm.
I would be interested to know why you are expecting to output at UK settings 230Vac rather than USA 120VAc.

Should we assume you are off grid with a UK fridge etc?

Last night i looked at a youtube video for your sms TL US series and it showed the 2 strings separately... whilst highlighting the each panel group graphic on the display.
As above a photo would help.
Your best bet is to contact SMA-America, the uk/German guys were great.
Contact - http://www.sma-america.com/home-systems/contact.html

Nev
 
Your original post at 2:20 am UK time (BST) suggests you were up late or that your location is correct e.g. California and your time was 6 or 7pm.
I would be interested to know why you are expecting to output at UK settings 230Vac rather than USA 120VAc.

Should we assume you are off grid with a UK fridge etc?

Last night i looked at a youtube video for your sms TL US series and it showed the 2 strings separately... whilst highlighting the each panel group graphic on the display.
As above a photo would help.
Your best bet is to contact SMA-America, the uk/German guys were great.
Contact - http://www.sma-america.com/home-systems/contact.html

Nev
It seems I didn't include enough info.
I'm in the US with 220VAC output from the Sunny Boy - all the dials are set to "0".
The unit is producing power as designed.
All the panels are on one string due to the voltage required (170VDC as I remember). If the panels were split, it wouldn't trigger on occasion.
The question is how to get the panel to show 220VAC output that it is producing.
I'm sure SOMETHING has been left out here ... LOL
 
We are confused, normal US supply is 110V? Why are you expecting your Inverter to output 220V?

When correctly set up it is designed to match Grid Voltage and Frequency (US 110V 60Hz, UK 230V 50Hz)

When the inverter boots up it displays its configuration standard.

Disconnect the grid to it (isolator or breaker) and then isolate the dc supply (worst case pull the SMA 'Sunswitch' DC link out of the bottom) then reconnect the DC and then the AC - the order is important as you don't want to disconnect or reconnect the DC under load
As the inverter boots up it will display the grid connection standard that it is configured to (UK gnerally is G83/2 = 230V, 5oHz)
I doubt that the display is wrong, more that you are expecting a different reading.

When we know the standard that the inverter has been configured to we can advise on what Voltage output it would give.
 
.duplicate post deleted
 
We are confused, normal US supply is 110V? Why are you expecting your Inverter to output 220V?

When correctly set up it is designed to match Grid Voltage and Frequency (US 110V 60Hz, UK 230V 50Hz)

When the inverter boots up it displays its configuration standard.

Disconnect the grid to it (isolator or breaker) and then isolate the dc supply (worst case pull the SMA 'Sunswitch' DC link out of the bottom) then reconnect the DC and then the AC - the order is important as you don't want to disconnect or reconnect the DC under load
As the inverter boots up it will display the grid connection standard that it is configured to (UK gnerally is G83/2 = 230V, 5oHz)
I doubt that the display is wrong, more that you are expecting a different reading.

When we know the standard that the inverter has been configured to we can advise on what Voltage output it would give.

Yes 110VAC 60Hz is normal (or perhaps 117VAC) and 220VAC is expected leg-to-leg. Actually, higher than 220VAC due to the push method that Sunny Boy uses. If the display is correct, maybe it's per leg. I'll check on that.
 
In the US you are supplied with 2 phases (legs) and a neutral. Eg 2 x 110 at 60hz. Between the legs(phases) you see around 210Vac, typically used for your larger appliances e.g. oven/cooker or aircon.
If the US inverter is connected to one leg(phase) it will see 110Vac at 60hz and match that. So the inverter is correctly measuring the voltage. I would trust the inverter.
My inverter was ramping up the voltage to match the mains, nominal 230Vac(212-253)... it was sending 264Vac and shutting down. [It looks like my inverter is set to the old 240(220-263 volts range UK standard). An engineer fixed the village supply back to 240 as it showed the maximum allowed of 253Vac at night when noone was generating.
I repeat... i would trust the inverter and measure the voltage where mains cable goes into the inverter... not leg-2-leg somewhere else.
On another note. Do you have a generation meter? Do you receive payments from the city/state for the energy you generate like we do here in the UK?
 

Reply to Intermittent disturbance on Sunny Boy inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
864
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi, Recently had 3.6kw solar installed, at the time shortage of batteries & roi figured batteries not quite worth it. thinking otherwise perhaps...
Replies
5
Views
2K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock