But if the cpc is connected from the appliance to new cpc plus old cpc as well as the CU end the cpc should be continuous up to the point of loss of contact... But on both ends. Although if there were 2 losses in contact along the length..
Obviously the op said it would be easy to replace so has done a bit of service by providing protection against exposed parts so therefore is a reasonably good temp fix

Your assuming the old cpc is good until the old connection. It might have failed 100mm from the CU.
 
the CPC for the circuit will be routed with the live conductors (or in close proximity - in back boxes) along it's entire length.
Kitchen was refitted 3 yrs ago and no docs available so they extended original cooker cable prob from the switch which is now tiled over somewhere.
This suggests the two cables don't share the same routing. I don't think anyone making the alternative cpc connection can say for sure.


As for sleeving yellow/green with brown in a flex... that's not weird, it's plain wrong. If you need three live cores you should be using an appropriate 4 core flex
Have you got a reg for that? The only one i know of forbids over sleeving of a single green yellow. The only way it would be forbidden for multi core would be if the two flexes run together were considered separate wiring systems and the cpc in the other not being in close proximity.
Even then, you could theoretically run a separate cpc like you would with swa sub mains, although i doubt it's done ever!
if the cooker circuit had no cpc whatsoever, would taking a connection from the RFC to provide a cpc be correct, according to the regs mentioned?
Possibly, if they run together throughout the circuit, assuming two t&e together are considered the same wiring system.
 
This suggests the two cables don't share the same routing. I don't think anyone making the alternative cpc connection can say for sure.

I disagree, his post suggests the cable was extended at the original switch meaning there are two cable segments, one from the CU to the switch and another from the switch to the cooker. Both segments will be wired in T+E (valid assumption) meaning the CPC is contained within the wiring system (the cable, again... valid assumption).

And thus, it's not breaking any regulations.

Have you got a reg for that?

No, I don't have a reg for that. It's my personal take on what I consider to be good practice. If there is an earth in the cable, use it for the CPC or don't use it, don't sleeve it and use it for something else. There's not many occasions I can think of where you'd have an earth in a cable and not use/require it as an earth/CPC. The only one that springs to mind is light fittings and supplying class two equipment. In all other cases I would use x+1 core cable where x is the number of live conductors I required.

For the most part, these appear to be matters of opinion and interpretation. You've got your interpretation and opinion and I've got mine, it's unlikely we are going to agree, but then I don't have to agree with you, I just have to be happy with my interpretation of the regulations and their subsequent application.

So, as usual I think you and I are going to have to agree to disagree.
 
I disagree, his post suggests the cable was extended at the original switch meaning there are two cable segments, one from the CU to the switch and another from the switch to the cooker. Both segments will be wired in T+E (valid assumption) meaning the CPC is contained within the wiring system (the cable, again... valid assumption).

And thus, it's not breaking any regulations.
.

But you are assuming the break/fault is at the original switch, it could be elsewhere. You would have to assume it is not continuous from the CU. Therefore it is not complaint.
 

Reply to Is a borrowed earth allowed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
675
Good evening all, So been to an upstairs flat today I East ham, the entire road is terraced 2 storey building which look like a row of terraced...
Replies
9
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
915
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock