Hi all,

I'm technically a 'trainee' but in a months time I will finally have all the qualifications to apply for an approved electrician jib card.

The first job I will be undertaking is getting a house up to HMO requirements, which are outside the scope of bs7671 so it's all a bit alien to me.

I know the areas I need to cover with emergency lighting, but I'm unsure as to the requirements of a key switch?

The existing lighting installation is obviously wired in two core so the key switch would do exactly the same job as the breaker.

Any advice would be most welcome.

Thanks!
 
An identified test facility is required for routine testing.
 
To reply OP use the box at the bottom, to reply to someone just tap/click on the "reply" on their Post that way other members can see your reply.
In reply to your pm to me a protective devise would also isolate the general lighting which could be hazardous.
 
To reply OP use the box at the bottom, to reply to someone just tap/click on the "reply" on their Post that way other members can see your reply.
In reply to your pm to me a protective devise would also isolate the general lighting which could be hazardous.

Sorry!

I was under the impression you could install emergency lighting in an an existing two core circuit and switch the permanent line for emergency lighting tests.
 
What do you mean by two core circuit I assume you mean two core and cpc. Yes that is the normal way to isolate the charge/ permanent conductor through a test facility.
 
Yea two core as in permanent line from the board, looped through the fittings and spurred out to emergency fittings.

In a new installation I've always installed three core so the test switch only activates the emergency fittings and leaves the others on.

In this installation breaking the permanent line will cause all the light fittings to switch off (other than the emergencies). Which would be safe as all relevant areas will be covered by emergency lighting and all rooms have natural light.

But you said 'a protective devise would also isolate the general lighting which could be hazardous'
 
How many em lights are there, you could always put in individual test facilities from each fitting.
 
Sorry!

I was under the impression you could install emergency lighting in an an existing two core circuit and switch the permanent line for emergency lighting tests.

That would be a very poorly designed installation, and possibly not compliant with the emergency lighting standards.
 
I was assured that you can retrofit emergency lights into an installation wired as I said, is there any regulation you can give me that contravenes this? I'm really struggling to find any information about it hence asking the question here.
 
I was assured that you can retrofit emergency lights into an installation wired as I said, is there any regulation you can give me that contravenes this? I'm really struggling to find any information about it hence asking the question here.

Assured by who?
You'll find it in BS5266, I haven't got a copy to hand at the moment but you presumably have access to it if you are designing an emergency lighting installation?
 
In short, there's nothing stopping you from tapping off of the local lighting circuit to each individual fitting and using a breaker as your test facility. You better have a decent risk assessment in place however to justify this, plus a clause within the O&M manual making it clear that any testing must only be done during daylight hours.

If the client or one of their representatives decides to carry out a monthly test on them in the dark and falls over, you will be sued that's a guarantee.

I'd highly recommend you obtain a copy of BS5266 and learn it by rote because there is an awful lot to designing a compliant emergency lighting system, even if it's only a few cheap bulkheads in a three bed semi. An awful lot that I get the feeling you haven't even begun to consider.
 
  • Agree
Reactions: Fordango
Yep, I think you might be right on that one, I've installed many emergency lighting systems in the past but never designed them.

I had no intention of carrying out the work before I was fully confident in what I was installing, that's why I came here for advice.

If the advice is buy BS5266 and fully understand it's requirements then that's what I'll do, even if it will be the yellow version that'll only be useful as toilet paper next year...

Thanks for the advice.
 
Buy the full version and not just the guide. As a designer the guide won't be enough.

I'd also recommend some decent software such as relux and draftsight/cad as you can effectively kill a number of birds with one stone when it comes to presenting design information, manufacturers data, calculations, lux levels and floor plans.

Also, if you're planning on doing emergency lighting design correctly, be prepared to lose out on 95% of your quotes to other sparks who think that just slinging some EM lighting in and hoping for the best suffices.

Essentially, if you're doing it correctly, expect that with even the smallest of projects you'll be handing over a reasonably hefty folder to the client containing all the above birds killed and more.

Below is part of a recent project of ours on Relux:

17436162_1389244854483193_6680512099529316964_o.png.jpg
 
  • Like
Reactions: westward10
You don't necessarily have to buy a copy of a British standard, access to it is free via your local library. for a one off small job it may be a more sensible way to go.
 
It's more than likely not economically viable to carry out a one off small EM lighting job if you're looking to comply fully with the requirements of BS 5266
 
Depends what type. Neither are really cost efficient for small installations, and for a stand alone self test system the results will still need recording by someone competent to do so.

For a larger installation a centrally controlled ATS would be a much bigger outlay, but over the years could potentially save on maintenance costs.
 
Can’t you just mount a single patress / key switch next to the consumer unit.
Take out the live from your breaker and connect it to L1 of your key switch and then connect a new live from the breaker to the com of your key switch.
It’s no different to just switching the power supply off to the light circuit but at least the customer doesn’t touch the mcb.
In an ideal situation you would have a 3 core circuit so the key switch would have its own permanent supply to the emergency light but as long as testing is done during daylight hours and you specify this especially in the test log book.
 
Old thread, but valid advice.
 
Can you not use self test emergency lights in this scenario
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Is a keyswitch required for HMO emergency lighting?
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
flex_m,
Last reply from
Admin,
Replies
20
Views
6,601

Advert