h34thy

Hi everyone
I'm reading all I can at the moment on inspecting & testing, I'm reading Chris Kitchers Practical Guide to Inspection, Testing & Certification, first ed.

I'm on page 95, step 1 of measuring PFC. It says "Place the phase lead on the supply side of the main switch and the neutral and earthing probes/clips onto the earthing terminal" now opposite that in the picture on the same page it says "Joined leads (which I'm guessing is the neutral and earthing probes/clips said in step 1) at neutral at supply side of main switch. I'm sure I'm not mistaken in saying that's a mistake in the book.

Does anyone agree or am I missing something?

Cheers!
 
Hey mate some meters require you to join neutral and earth (2 wire tester) for PSSC.

my fluke 1652 for instance does not require you to connect them together.

You might be getting confused between PEFC and PSSC

PEFC = L-N-E 3 lead test
PSSC = L-N/E 2 lead test
 
1st might be for pefc and 2nd for pscc. but there are some mistakes in that book. this might be 1 of them.
 
Just got a bit confused guys,

There's steps 1 - 3 for connection for 2-lead instrument
and
There's steps 1 - 2 for connection for 3-lead instrument

For 2-lead instrument it says in writing & pic red & black probes to supply side of main switch.

For 3-lead instrument in writing it says "Place the phase lead on the supply side of the main switch and the neutral and earthing probes/clips onto the earthing terminal".
But in the pic it shows you black and green croc clips clipped together and placed on the neutral terminal supply side of the main switch and red probe on the live terminal of the supply side of the main switch.

Test instructions for PSCC are on next page.

Not doubting your knowledge guys just abut confused.

Has anyone got the book? Plus think there's another cock up on page 101 lol
 
can't comment on fluke and metrel testers as i use a megger, and that's always a 2 lead test. only use 3 leads for no-trip efli testing. and as archy says, there's a few errors in that book. go by your mfts crib sheet.
 
so now we have 3 line motors????? methinks the suits at IET are just altering terminology to justify their existence and buy new ipads.
 
Will do mate when I get one, just trying to stock up on as much knowledge as poss to get myself ready for 2391 or 2394/95.

I'm thinking of getting one of the fluke multimeters, could anyone recomend which one?
 
Why bother with those books? I'm sure Mr Cockburn will have a self published 15 page comic I mean explanatory document giving all the information you need
 
yeah. 1552/3, that's a megger made by megger, used to megger, no flukes about it.
 
I'm thinking of getting one of the fluke multimeters, could anyone recomend which one?

A 'multimeter' is a different piece of kit entirely. What you're in the market for is a 'multifunction' tester, specifically a 17th edition one. There are a few different makes, but I'd say that the Megger probably have the edge in popularity.

Cheers
 
Multimeters
Fluke
Megger
Metrel

These are the 3 most common

As for 2 lead or 3 lead me thinks the author is covering his self because some testers ie the older units have a 3 lead set up the newer ones are 2 lead
 

Reply to Is this a cock up in this book? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top