Go on. ? ? ?Have just thought of another benefit a ring installed in this manner might have over a 32A 4mm radial: a ring would have more flexibility regarding its method of installation.
Discuss 'Leapfrog' wiring of a ring in a long workshop. What do you think? in the UK Electrical Forum area at ElectriciansForums.net
Go on. ? ? ?Have just thought of another benefit a ring installed in this manner might have over a 32A 4mm radial: a ring would have more flexibility regarding its method of installation.
A 32A 4mm² radial could only be installed ref method C if T&E, or if singles in conduit/trunking method B or C. Other ref methods would bring the cable CCC below 32A.Go on. ? ? ?
Was just trying to understand yor reasoning PM that's allA 32A 4mm² radial could only be installed ref method C if T&E, or if singles in conduit/trunking method B or C. Other ref methods would bring the cable CCC below 32A.
On the other hand a 32A 2.5mm² ring can be installed ref methods A, B, C, 100, 102 if T&E, or A, B, and C if singles in conduit/trunking.
But I think you already know this
The rails are called purlins, and you can buy plastic covers to go over cables in them. No idea where you can buy the covers from, but I've seen them in use.... fitting 13A/16A sockets on each of the horizontal 'top hat' wall rails ...
The plan is to convert uninsulated agricultural stores into pleasant office-like environments which I can rent out.
This building is not for multiple occupancy.
Agreed. That was badly-written at 01.00.If the distribution circuit is protected at 40A you might want to avoid 32A final circuits and go for 20A radials instead.
This apparent contradiction was somewhat confusing as to the application:
You don't (or at least, probably do not) need 4mm for a 25A radial - even less so for a 20A radial. You can do HI earthing just by running a separate earth to the far end of the radial.I'm going to protect these 13A socket rings at 25A, or even 20A. The sole reason for using a ring was to avoid the hassle of terminating 4mm, and to give high-integrity earthing.
And terminating the cpcs in separate terminals in the socket outlets, and terminating the cpcs (if it's an RFC in separate terminals in the CU)You don't (or at least, probably do not) need 4mm for a 25A radial - even less so for a 20A radial. You can do HI earthing just by running a separate earth to the far end of the radial.
I never had any intention of protecting at 32A, for, as you correctly surmise, discrimination up-stream.
I'm going to protect these 13A socket rings at 25A, or even 20A. The sole reason for using a ring was to avoid the hassle of terminating 4mm, and to give high-integrity earthing.
Stuff all. It’s a big airport machine but has only a 13A plug.Make sure you check the power requirements for the 'big x ray machine'
Stuff all. It’s a big airport machine but has only a 13A plug.