A 32A 4mm² radial could only be installed ref method C if T&E, or if singles in conduit/trunking method B or C. Other ref methods would bring the cable CCC below 32A.

On the other hand a 32A 2.5mm² ring can be installed ref methods A, B, C, 100, 102 if T&E, or A, B, and C if singles in conduit/trunking.

But I think you already know this ;)
 
A 32A 4mm² radial could only be installed ref method C if T&E, or if singles in conduit/trunking method B or C. Other ref methods would bring the cable CCC below 32A.

On the other hand a 32A 2.5mm² ring can be installed ref methods A, B, C, 100, 102 if T&E, or A, B, and C if singles in conduit/trunking.

But I think you already know this ;)
Was just trying to understand yor reasoning PM that's all
 
Crikey this has all kicked off while I've been away :)
Thanks for your interest. There are many valid questions to which I'll reply properly tomorrow.

To make it all a bit clearer, here's a picture of the existing unfinished workshop.
DSC_1020.JPG

I'll be using the central 'top hat' purlin as a cable way. The DB will be at the far end. There will be a variety of sockets and other accessories in one straight line on each long wall.

Here's a picture of a corner of my other, finished, workshop which has exactly the same structure as that above. Note how the accessories follow the line of the top hat rails.
DSC_1018.JPG

The plan is to convert uninsulated agricultural stores into pleasant office-like environments which I can rent out.
It's amazing what a bit of Celotex and plasterboard, some sticky foam and Tek screws can do.
 
Had another thought ...
How about doing the sockets in groups by bay ? The the ring would go CU - bay 1 - bay 3 - bay 5 - bay 4 - bay 2 - CU. At least then all the sockets in one bar will be on one leg of the ring so less confusion, but you avoid the "long leg" issue.
As you work on a bay, you just need to leave two tails long enought to reach their next sockets and join then in a JB.
Another option apart from a ring would be two raduals in 2.5mm on a 25A breaker (assuming impedances allow, and check cable capacity vs insrallation method ). Link the CPCs at the far end and you can have high integrity earthing and it will improve the EFLI. If this is intended to be office spave then you might want to consider HI earthing and more circuits. A large quantity of IT on one circuit can be problematic in a number of ways. At one past job, we could not power up one circuit unkess we turned the copier off first - that was due to to total inrush current of all the computers, with the copier tipping it over the edge for the B32 breaker.
Thinking a bit more, you coukd do one 25A radial/bay, and run a 4mm earth (if it's mechanically protected) to pick up the far ends of each circuit's CPC. Gives you segregation (c.f. all eggs in one basket) of loads, and in fact a much higher total load capacity.
 
Leapfrogging! - pretty standard practice, however;
I think if you are renting out individual office space, it might be wise to consider them as individual circuits as the inconvenience of one office 'tripping off' affecting another office might not be greatly appreciated.

Apart from some of the other issues listed by others, a horizontal purlin rail rail makes a great vermin run and pvc t&e might not be the best choice!
 
As it's going to be office space presumably with different companies in each bay, it reinforce's my and others opinion that you ought to run separate radials to each bay with IMO RCD protection for each bay and a clean earth installation.

I have come across this sort of rented office space before and most of them have a reception with telephone operator and a meeting room, this gives the possibility of shared office's by different companies, more use and revenue, the possibilities are endless.
 
Yes, if the bays are used by different organisations I would make them electrically independent so that one user with a faulty appliance cannot disrupt another user's work. This was not clear from the original description: '...replacing the wiring, in one of my own (metal, agricultural-type) workshops.'
 
Good morning
Wow this has gone off an various tangents! Sorry for the silence - I've been outside digging holes, as one does.
This building is not for multiple occupancy. If it were, there's no way I'd 'share' circuits, that would be terrible design.
It's not that big - just one open 'shed' 20m x 8m, built in steel with standard 4m bays, to be used for rental to engineering companies who use it for specialist research projects. None are particularly power-hungry: a few computers, printers, the occasional big X-ray machine, data acquisition kit, and a few power tools. All under my supervision.
It's not like I'm going to let the buggers plug in a dc Turboencabulator.
The building is remote and has only a 40A per phase supply. I only want loads of sockets to give flexibility and discourage extension leads. Looks pro too :)
I'll also put in a few 16A 3 phase sockets and supply distro boxes to give a choice of phase in use, to balance the load.
 
If the distribution circuit is protected at 40A you might want to avoid 32A final circuits and go for 20A radials instead.

This apparent contradiction was somewhat confusing as to the application:

The plan is to convert uninsulated agricultural stores into pleasant office-like environments which I can rent out.
This building is not for multiple occupancy.
 
If the distribution circuit is protected at 40A you might want to avoid 32A final circuits and go for 20A radials instead.
This apparent contradiction was somewhat confusing as to the application:
Agreed. That was badly-written at 01.00.

There are three buildings. Each forming one 'environment.'

I never had any intention of protecting at 32A, for, as you correctly surmise, discrimination up-stream.
I'm going to protect these 13A socket rings at 25A, or even 20A. The sole reason for using a ring was to avoid the hassle of terminating 4mm, and to give high-integrity earthing.

My original question was about only what I used the made-up term 'leapfrogging' for, ie the 1-3-5-7-9 / 2-4-6-8-10 wiring technique!
[automerge]1592222049[/automerge]
Here's a pic of the first bay in 'Building B' which I converted this Feb.

The position of all the accessories is directly in front of the middle purlin. Once finished it's sealed both ends in each bay to keep vermin out. (I hope!)
DSC_1035.JPG
 
Last edited:
I'm going to protect these 13A socket rings at 25A, or even 20A. The sole reason for using a ring was to avoid the hassle of terminating 4mm, and to give high-integrity earthing.
You don't (or at least, probably do not) need 4mm for a 25A radial - even less so for a 20A radial. You can do HI earthing just by running a separate earth to the far end of the radial.
 
You don't (or at least, probably do not) need 4mm for a 25A radial - even less so for a 20A radial. You can do HI earthing just by running a separate earth to the far end of the radial.
And terminating the cpcs in separate terminals in the socket outlets, and terminating the cpcs (if it's an RFC in separate terminals in the CU)
 
I never had any intention of protecting at 32A, for, as you correctly surmise, discrimination up-stream.
I'm going to protect these 13A socket rings at 25A, or even 20A. The sole reason for using a ring was to avoid the hassle of terminating 4mm, and to give high-integrity earthing.

Ah but you said ring, and the only standard ring circuit in the book is a 32A ring circuit, a 25A or 20A ring circuit is non-standard and for most installations quite pointless so we all assume that a ring final circuit will be a 32A circuit.
 
If you did put the Ring on a 20A or 25A seems you'd have the benefits of a Ring and Radial together in conjunction with the Leapfrog wiring method - thinking about it I can't see any drawbacks?

and again if you did use 4mm I say the same?

Sorry I skimmed the thread - this is fixed load stuff? Seems quite sensible?
 

Reply to 'Leapfrog' wiring of a ring in a long workshop. What do you think? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
1
Views
439
I've purchased Lepro 15m LED strip lights - product code PR410047-RGB-UK, and have fitted them at the top of the walls in my daughter's bedroom...
Replies
9
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock