Brief run down for you all

Checked end to end of ring that’s sound
Meggered LN sound NE sound LE 0.03

Split the ring same stuff
Split it again same stuff again

Long story short stripped all sockets off on the ring and every single leg has a LE fault

Was rewired 2010

Only logical thing I can think is just a bad drum of cable was used ?
The CU is a screwfix off brand thing so one can only assume it is screwfix special T&E used

Anyone got a better suggestion please let me know left me scratching my noodle for a while

EDIT:
there are no neons
The cable is twin and earth 2.5mm
All sockets were removed ring completely split at every outlet
 
Last edited:
if those readings are in Megohms, the 3.48M is acceptable. the 0.03 looks like a neon. hidden FCUs?
 
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
 
That is sounding very much like bad cable. Odd it is just the L but presumably it could have been the brown PVC mix that was contaminated in some way.

I wonder if it was like that new and the installer just ignored it, or if it has gone bad with time?

The rented "anti vandal site office" we have just is a bit like that, but all circuits in the 0.2M region for both L-E and N-E even though not much T&E. Not ours to fix though :(
 
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
Every thing is disconnected pal literally just legs out the wall and every single leg has a LE fault some 0.03M next one coul be 0.59M one leg was 3.38M but every single leg was faulting
 
Can you get enough of the T&E to read the manufacturer's details, etc? Wonder if there is any site with recall information on bad cable.
 
Surge protected extension leads still plugged into each separated section?!
Can you get enough of the T&E to read the manufacturer's details, etc? Wonder if there is ant site with recall information on bad cable.
Not at the minute left my suggestion and findings with homeowner he’s ringing home insurance to see if he can get them to foot the bill 😂
 
That is sounding very much like bad cable. Odd it is just the L but presumably it could have been the brown PVC mix that was contaminated in some way.

I wonder if it was like that new and the installer just ignored it, or if it has gone bad with time?

The rented "anti vandal site office" we have just is a bit like that, but all circuits in the 0.2M region for both L-E and N-E even though not much T&E. Not ours to fix though :(
I thought the same about the installer like don’t get me wrong board was tidy sockets made off neat decent looking job from what I’ve seen, but I’m sure LE readings would have been down from install on a faulty drum ? 12 years is a rapid decline.
I’ve asked homeowner for test results if any were provided like there’s no name on board no stickers or ote like that basic stuff but usually a tell tale of someone who isn’t fully legit
 
I doubt that if it was the fault would be shown before that the only way split the cables.
I doubt that if it was the fault would be shown before that the only way split the cables.
Sorry I feel I must have worded it poorly but I did mate I took every socket off and every leg between every socket had a LE fault my thinking was the drum must have been
NE >999
LN >999
LE >50

Something like that at install so it would have held fine and now 12 year down line it’s broke down and obviously a shitty LE anyway Would explain every leg having the same fault
 
The only possibilities are really
a) cable faulty
b) VERY wacky wiring, e.g. everything connected back to one point somehow
c) MFT suddenly faulty (I guess you have repeated earlier good readings to rule that out already)
Everything else (flood, rats, plasterers, plumbers) wouldn't consistently only affect live.

I'm sure most of us would be interested in the outcome of this one as it's rather a nightmare for you and customer.
 

Reply to Live earth fault on every leg of the ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
462
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
927
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock