I guess the point is you can have T&E without RCD protection so long as it is not hidden < 50mm from a surface.

Feeding a CU off a 32A MCB works, but is not terribly good either as any big fault is likely to trip both the CU and the feed MCB, but again depending on what is needed that may or may not be a concern. Certainly I would be looking at a couple of RCBO in such a 2nd CU to reduce the chance of something on the sockets also taking out the lights.

But what is lacking here is the design aspect - what sort of load(s) are expected, etc. If it is just lights & sockets then a 32A feed is plenty, but if there is going to be an electric showed that suddenly looks small.
No shower the shower will be thermostatic just 8 sockets , the only thing I can think is they have a walk in wardrobe where could possible be a hair dryer and other things like tht on at the same time , but I’m thinking taking a 10mm t+e to a sub consumer unit which will be fitted close by to the existing CU and won’t be buried fit an RCD protected 2way CU one sockets for sockets one for lights ?
 
Why not fit the sub CU in the loft, then if it trips the recommended RCBO's in the sub board its not a trip all the way downstairs to re-set.
 
Why not fit the sub CU in the loft, then if it trips the recommended RCBO's in the sub board its not a trip all the way downstairs to re-set.
Why not fit the sub CU in the loft, then if it trips the recommended RCBO's in the sub board its not a trip all the way downstairs to re-set.


It’s a weird one mate would be ideal to do that but the existing CU sits on the ceiling in the hall which above that will be the middle of the bedroom upstairs so planning to fit the Sub Cu beside the existing one basically and run the circuits through the ceiling and under the new floor to where they need to go
 
Why not fit the sub CU in the loft, then if it trips the recommended RCBO's in the sub board its not a trip all the way downstairs to re-set.
It’s a weird one mate would be ideal to do that but the existing CU sits on the ceiling in the hall which above that will be the middle of the bedroom upstairs so planning to fit the Sub Cu beside the existing one basically and run the circuits through the ceiling and under the new floor to where they need to go
 
Post 11 page 1. Echo, Echo, Echo, Echo, Echo

No need for a submain and new dist board just for a couple of lights and a few sockets. Just extend upstairs lighting circuit and upstairs RFC. Why over complicate things?
 
Like I stated existing circuuts are all in conduit and instead of tapping in to them I wish to run new socket and lighting circuits
I'd sooner tap into them than bodge "new circuits" into a full consumer unit. If you want new circuits change consumer or add a new one. If not, tap into the existing lighting circuit and ring. If exisiting consumer unit doesn't have RCD protection, that's something else to deal with for the additions.
 

Reply to Loft conversion help? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. We live in an older house and we are doing a loft conversion. We do not have an SPD on the connection to the grid and the builder's...
Replies
49
Views
5K
Hi. I was asked to work on a loft conversion and a full refurbishment of a 5 bed house. The contractor said that as he is doing a loft...
Replies
11
Views
2K
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...
Replies
3
Views
1K
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K
Hi fitting a a couple loft sockets on a radial circuit. I only have 2.5mm cable and really don’t want to buy a reel 4mm2 is it ok to use on 32A...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock