on a ring testing Insulation Resistance L-N shows 0.63 Mohms
but L-E is ok.
I checked with the home owner that nothing was switch on, nor plugged in still.( its a 3 bed semi, looked every nook and cranny)

Is that kind of reading tell tail of anything causing that in particular, or is it a case of next visit to investigate each socket and feed to/between it individually?

Reason is they are getting random trips of the RCD for that circuit. BUT on a different circuit (hot water tank) MCB it was tripping out the RCD only when switching on the heater element , BUT NOW isolated that, and it still ocasionally trips same RCD when i.e. turn on toaster (happened once) or garage lights (happend once), also a few times when no appliance/switche were touched, both on different circuits but same RCD.

I've checked the trip out times and manual function of that RCD:

1/2: a/c tripped out, reset and never tripped on this setting after re-trying later numerous times.
1/2: d/c didnt trip

1: a/c 34ms
1: d/c 29

5: a/c 9
5: d/c 7

Its an MK RCD standard usual, Megger 1552 on 30mA setting

Heater tank circuit tested ok, and kitchen ring tested ok.

Thanks in advance
 
Last edited:
lift the sockets off the boxes and check all. . even a bit of damp in a wall can cause tracking across terminals. if still low readings, then split ring and test each leg, then split faulty leg and so on.
 
As telectrix said any damp would cause a problem with ir readings, as explained the only way to diagnose is to split ring up then keep adding until fault is found.
 
As telectrix said any damp would cause a problem with ir readings, as explained the only way to diagnose is to split ring up then keep adding until fault is found.

well, at least that solution is less drastic than your previous post of a rewire. LOL.
 
that's something that can only be determined by on site inspection/test.
 
and if the wiring is not too old: has not been attacked by rodents, 90% of the time, the fault will be at an accessory. damp, trapped/squashed cable, faulty accessory. even a loose connection could cause the fault.

edit: included with rodents are plumbers, builders, wood butchers with their blowlamps, hammers, and nails.
 
Last edited:
not always. cores are split at accessories, so there could be a L-N fault which does not affect the cpc.
 
Good point, but personally I wouldn't say that damaged insulation at an accessory meant a rewire was required as had been previously suggested,but perhaps that is why I'm not rich.
 
it's all hypothetical as without being on site without test gear it's guesswork.
 
on a ring testing Insulation Resistance L-N shows 0.63 Mohms
but L-E is ok.
I checked with the home owner that nothing was switch on, nor plugged in still.( its a 3 bed semi, looked every nook and cranny)

Is that kind of reading tell tail of anything causing that in particular, or is it a case of next visit to investigate each socket and feed to/between it individually?

Reason is they are getting random trips of the RCD for that circuit. BUT on a different circuit (hot water tank) MCB it was tripping out the RCD only when switching on the heater element , BUT NOW isolated that, and it still ocasionally trips same RCD when i.e. turn on toaster (happened once) or garage lights (happend once), also a few times when no appliance/switche were touched, both on different circuits but same RCD.

I've checked the trip out times and manual function of that RCD:

1/2: a/c tripped out, reset and never tripped on this setting after re-trying later numerous times.
1/2: d/c didnt trip

1: a/c 34ms
1: d/c 29

5: a/c 9
5: d/c 7

Its an MK RCD standard usual, Megger 1552 on 30mA setting

Heater tank circuit tested ok, and kitchen ring tested ok.

Thanks in advance
I'd say there is something connected you haven't found
 

Reply to Low Insulation Resistance reading of 0.63 MOhms , what does this indicate? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
990
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
781
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
802

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock