Hi All,

After some information, I have a friend who is a landlord, they recently had a battery powered smoke alarm installed in the flat with the local fire brigade,however fire brigade found out it was rented accomodation and have written to local council to say a mains smoke alarm is required to be installed.
My questions are,

I am an Approved spark so can i install a mains smokie by tapping into the lighting circuit at the DB? and would a minor works certificate be required for the installation? can i do it myself or because if it needs certified and the council are aware would my friend have to get an electrical contractor to do it?

Any help appreciated

Cheers

Dexy
 
Hi dexy,

If you are running the smokes from an exsiting lighting circuit, you will also need to run it through an fcu, so they can be isolated without turning off the lights aswell. As for notifying, as long as there not installed in a kitchen or bathroom (which they shouldnt be), then they shouldnt need notifying (I could be wrong on this), but you will need a MWC and a smoke certificate.

Jay
 
I don't connect through an FCU, nor do I provide a smoke certificate. If its 2 story, you will need coverage downstairs and up on the landing and they need to be linked. Link either by 3core&e or radio link. Then provide a MWC.
 
Glad to hear the fire brigade are on the ball

You need a MWC- if its adding to an esxiting circuit or an EIC if it's a new circuit (checking the bonding status etc)

The preference now is a reguarly used lighting circuit so the tenants can't switch a MCB off or pull a fuse to isolate the smoke detector alone

You will need to give a BS 5839 Pt 6 certificate as well

No notifying stuff required as no part P in Scotland
 
I don't connect through an FCU, nor do I provide a smoke certificate. If its 2 story, you will need coverage downstairs and up on the landing and they need to be linked. Link either by 3core&e or radio link. Then provide a MWC.

I also dont connect via a fcu but thats what it says in the bgb. I try and fit them on there own circuit either on the none rcd side of a board, or via an rcbo. But I do give the client a smokes cert, looks more professional and in this case, the council may want to see one. The last house I put some in, had just had there loft converted and the labc told them to either fit a fire door, or fit a smoke in the loft and every bedroom and on the landing up and down, 6 in total. Overkill IMO but the customer said fit them and when the labc have been and ok'd it all, he would remove all the ones in the bedroom and just have the attick and landing ones.

I mean are the labc expecting the type of fires as in "Backdraft" lol


Jay
 

Reply to Mains Smoke Alarm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
347
i had a builder do some work but now my smoke alarms turn off when the lights are off, does this mean i can only have a fire when the lights are on?
Replies
9
Views
856
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
  • Locked
Required asap for price work. No of Workers: 2 Location: Brighton & Hove Description of Work: Installation of 230v operated, radio linked smoke...
Replies
1
Views
2K
Here we go again, another job that has had a council inspection, different council to last time but still perplexing. The problem with these jobs...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock