Discuss Max Zs /ADS / shared CPC & N in the UK Electrical Forum area at ElectriciansForums.net
Hey Everyone.
Whats your thoughts on using a 3core & earth to run x 2 final circuits? I have x1 three core & earth feeding contactors for emergency lighting. L1- fed from a 6A mcb is feeding a switched pole on a NO contactor, L2- fed from a different 6A mcb also feeding a pole on a NO contactor.
At the outgoing side of the contactor is x2 em lighting circuits, done in 1 5mm T&E. Now when calculating max Zs Im essentially using the same CPC for both circuits ( in the 3 core cable), which I don't like. Is it deemed safe/ normal practice to allow these essentially 2 circuits to share the same CPC & N. The DB is very close to the contactor board, so Im planning to run x2 new 1.5mm feeds to the contactors to gain true Zs readings.
Reply to Max Zs /ADS / shared CPC & N in the UK Electrical Forum area at ElectriciansForums.net
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
6K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...