0.40 Ohms
So wouldn't be achievable on a TT system, meaning disconnection times would need the use of an RCD so!!
Looking at 1 second disconnection times for distribution circuits, and 0.2 seconds for all others.
With a 100ma Rcd employed a max value of 500 ohms.
All that said, stability issues are considered relevant with anything over 200 ohms by BS 7671
Or as the NICEIC would advise (They make there own rules up) 100 ohms.
Final circuits are often quoted 1667 ohms when disconnection times are afforded by a 30ma rcd but thats generic and I personally prefer the tabulated values.
That's my take, hope it helps. :icon12: