Discuss MCB max load for an oven (EICR) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on an oven rather than a 32 amp. Is he right?
I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on oven rather than a 32 amp. Is he right?
Nope, a 40A MCB on a cooker feed is not an automatic fail. Why does he say it is?
No, he's talking ball hooks. If the cable is sufficiently sized for the CPD it can be any rating you want!
NB - lots of newer large range ovens with 5-6 induction hobs now require 40A and I've even seen 63A MCB's on 10mm cables
I'm not sure. Made no sense to me. I'll ask him tomorrow and post his reply. That's why I wanted to check the rules to see if it had something to do with the max consumption of the oven. Has anyone got a link to the rules so I can have a read?
Well, like any circuit, it depends on cable type, routing and device requirements
He said that because it’s not to regulation having a 6mm cable on a 40a MCB.
I actually found this answer below to a similar question on my builder.com (Is 6mm cable with a 40 amp MCB sufficient for a 8.5 kw electric shower? - MyBuilder - https://www.mybuilder.com/questions/v/38684/is-6mm-cable-with-a-40-amp-mcb-sufficient-for-a-85-kw-electric-shower), so it looks as though he's right.
"6mm twin and earth cable (which this almost certainly is) can be backed up by a maximum of a 32a MCB, even lower if other factors are involved. You'll need that 10mm cable and a 40a MCB unfortunately as your shower is going to draw over 32a. Whoever fitted the 40a MCB onto the 6mm cable originally was in the wrong."
The tabulated CCC for 6mm t&e (Clipped Direct) is 47A (Table 4D5)
There are other factors to consider and is not B&W, but its possible it is compliant!
he's wrong. 6mm cable ref. method C is rated up to 46A, so a 40A MCB is correct (if the shower/cooker draws > 32A but < 40A). only if cable is derated by refe.methof (insulation) does it warrant a 32A fuse, or even lessif need be.
Reply to MCB max load for an oven (EICR) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
I have an EV charger installed by a local firm. The install looks nice and tidy but with only a 2 meter run from the board you could hardly expect...
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...