have you got the leads on the place. If you have the earth lead on the live source and the live lead on the distributors earth then the tester will buzz and not test due to the touch voltage like IQ says because the metalic button is energised. Like wise you get the same problems when doing IR tests this way due to false readings to earth through your body if you pressing the metalic test button
Reply to Measuring Ze on a metrel MI3100 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Hi I’m just starting to do ev chargers so it’s looks like I need new tester. I currently have Megger 1711. So I can’t do a 6ma rcddc test. I...
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...