Discuss meger mft testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
J
james king
hi all
at collage we use the megger mft 1553!
now on a ring cct say 10m long we get a reading of 0.45ohms on sockets 1,2,3,4 but on socket no 5 the reading states 0.00ohms can any one give me some examples of what the metre will show upon faults?
i guess that the cables are twisted together in the back of skt 5, therefore the ring is still complete, however they are not connected in the bak of the skt plate, so u would remove skt plate to investigate! this is why u are prob getting no reading.
also did u swop the probes into neutral to check that it is not wired up in wrong terminals too?!
i take it u are testing R1+R2?
you don't say what you are testing. R1+R2? L/N? what?
i guess that the cables are twisted together in the back, therefore the ring is still complete, however they are not connected in the bak of the skt plate, so u would remove skt plate to investigate!
he's getting 0.00 not O/C, and cables should not be twisted
doesn't make sense. if reading 0.00, that's a dead short. remove socket no.5 and check connections. O/C = open circuit. btw.
if u reset the megger to 0.00 on and plug in than it will show 0.00 if no cct is made, therefore like i said earlier they are not connected in bak of skt.
does the little black gate on the screen of the megger show open or lclosed when u plug it into skt 5?
ahh ok ! just need to get use to the metre!
what are the 3 little circle at the top left with l-n l-e n-e or somw thing like that can remember of the top of my head?
they indsicate supply voltage and polarity. only come on when plugged into energised circiut. as said, look at megger tutorials on utube and practice with your tester till you can do it blindfold.
i dont think it is an open cct, like i said if the skt plate is not connected, the cct is still being made, but the terminals are not connected into the cct in skt 5, therefore the tester will still show 0.00 because it is not measuring anything!......do u not agree?!
so im still confuzuled???
open cct mean >99ohms
closed cct would give u a reading
IR
open circuit will give u >299
close cct (dead short) will give 0.00Mohms
can the megger tell you if the N is in L terminal and so on
sorry mate, too hard to explain on here, u need to be shown in real time. ask ur tutor to do it for u, if u pm me i have a dvd i can burn for u on megger testing and will send to u in post if thats any good to u?
Reply to meger mft testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...