Discuss megger 1553 in the Electrical Tools and Products area at ElectriciansForums.net
i=p/u
on the megger 1553 where is the ramp test selection. i think its the single triangle at top of selection.
how do we ramp test an rcd, isit at terminals for best results.
ps; never got instructions when bought. thanks
it is the triangle. just select the triangle. select the mA rating of the rcd under test.connect probes or use socket lead, press the test button. think it gives 5mA increments till it trips, then you read out the trip current. try it at home, preferably when eastenders is on.
All recorded tests, should be via the disconnected load side RCD terminals... Your testing the devise not the circuit!! Personally i would conduct a ramp test at the terminals too, or at least test once at the disconnected device and once, down line on individual circuits if your fault finding.
Did you not get the disc with your Megger?
you can download the manual free from megger website.
Reply to megger 1553 in the Electrical Tools and Products area at ElectriciansForums.net
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Hi, I have bought a new house. It has coax cables running to pretty much all rooms. I would like to replace these with cat6, and install new face...