M

midgetman

Went to house today. Rewired just 6 months ago. Tt - no rcd, ze 203. Low ceilings wanted metal light fittings added. 8 way consumer unit circuits tripled up in mcb. I said you need to get this sorted first. Contact the installer. Sorry but i'm not fitting the metal light fit tings which even a kid could reach. Real low ceilings cottage. Checked continuity of earth at existing lights was ok. Would you have fitted them?
 
I would not have fitted them as the house has no provision for ADS on earth faults and so is extremely dangerous.
In the case of a fault to earth every bit of earthed metal would remain live.
Assuming the fittings were class I fittings I certainly would not fit them in those circumstances, but then again I also would not do any electrical work in the house until it was resolved and would issue a danger notice.
 
  • Like
Reactions: 1 person
Shoot the dipstick who wired it
 
  • Like
Reactions: 3 people
did the owner of the property mention anything about the person that rewired it?
say, mebbe, that they arrived on a horse..?
 
No he probably tethered the horse at the OK corral
 
It's always a qualified spark supposedly. Usually described as "a proper electrician" but the clown didn't know what he was doing, if he ever existed.
I'd be willing to bet there were no certs or notification either.
 
anyway.to answer your original question.
no. I would not have fitted them. you made the right call.
 
That's £1200 house rewire for you, using a Mains board that's been in stock for a few years. No test certs no paper work. No cares. Please keep us updated. And no i wouldn't of changed the fittings
 
Thanks for the replies. The owner has contacted the original installer. Will be interesting what they have to say. Probably end up sorting out for them. We will see. Were not all cowboys in Cornwall lol :)
 
That's £1200 house rewire for you, using a Mains board that's been in stock for a few years. No test certs no paper work. No cares. Please keep us updated. And no i wouldn't of changed the fittings

If the house/owner is dodgy, our company would use red/blk cable and red tape etc.

No mate, never been there:D
 
Not disagreeing with any of the previous posts here, but, ......There are plenty of metal light fittings around that are manufactured to Class 2 requirements.
 
  • Like
Reactions: 2 people
If no Rcd was fitted,the chances are the installer was a potcher who knows "a lot about electrics"

Nothing new in that,except these days he may be signed up as competent
 
Not disagreeing with any of the previous posts here, but, ......There are plenty of metal light fittings around that are manufactured to Class 2 requirements.

Very true, but in a deathtrap like that common sense and risk management says just walk away. I wouldn't have fitted anything there. Problem being, what you do may not have made the situation any worse, but when someone gets electrocuted the name of the last person who worked on it is you so guess who ends up in the dock.

My question would be, is one under a duty of care to notify Building Control about it? If so, moral or statutory duty?
 
no RCD on a TT is an instant 2....so you wouldn`t be carrying out any work until adequate fault protection was in place...would you.

this could take the form of 100mA s type mainswitch with 30mA RCDs for the finals coupled with decent TT earthing arrangements (deep rod/s) for good, stable values of Ra..

just out of interest what was the Zs on the circuits in question?
 
Very true, but in a deathtrap like that common sense and risk management says just walk away. I wouldn't have fitted anything there. Problem being, what you do may not have made the situation any worse, but when someone gets electrocuted the name of the last person who worked on it is you so guess who ends up in the dock.

My question would be, is one under a duty of care to notify Building Control about it? If so, moral or statutory duty?

As i said not disagreeing with any of the above posters, just making a statement that not all metallic light fittings require an earth connection...
 
well...nearly as bad as the classic i went to deal with today....pendant hanging over bath....socket outlet next to bath ....no RCD and no crossbonding....no main bonding & no main earthing conductor....wallswitch in bathroom next to bath....various damaged fronts & boxes/enclosures etc...

well, put up an IP44 in the bathroom in place of the pendant....a pullswitch in place of the wallplate and got rid of the double outlet next to the bath by sending it through the other way )into the hallway)...oh, and put some supplementary bonding in that bathroom as well..

dealt with all the damaged fronts & enclosures.

put main earthing and bonding conductors in

gave it the dead tests on a condition report so the guy could get the supply reinstated

oh, and i forgot to mention that all the titywork that i came across in the bathroom was recent stuff...BS7671 hadn`t been anywhere near it...
 
They walk among us!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Metal light fittings.
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
midgetman,
Last reply from
Badged01,
Replies
25
Views
1,831

Advert