M
midgetman
Went to house today. Rewired just 6 months ago. Tt - no rcd, ze 203. Low ceilings wanted metal light fittings added. 8 way consumer unit circuits tripled up in mcb. I said you need to get this sorted first. Contact the installer. Sorry but i'm not fitting the metal light fit tings which even a kid could reach. Real low ceilings cottage. Checked continuity of earth at existing lights was ok. Would you have fitted them?
I would not have fitted them as the house has no provision for ADS on earth faults and so is extremely dangerous.
In the case of a fault to earth every bit of earthed metal would remain live.
Assuming the fittings were class I fittings I certainly would not fit them in those circumstances, but then again I also would not do any electrical work in the house until it was resolved and would issue a danger notice.
Shoot the dipstick who wired it
Reactions: 3 people
did the owner of the property mention anything about the person that rewired it?
say, mebbe, that they arrived on a horse..?
No he probably tethered the horse at the OK corral
It's always a qualified spark supposedly. Usually described as "a proper electrician" but the clown didn't know what he was doing, if he ever existed.
I'd be willing to bet there were no certs or notification either.
anyway.to answer your original question.
no. I would not have fitted them. you made the right call.
That's £1200 house rewire for you, using a Mains board that's been in stock for a few years. No test certs no paper work. No cares. Please keep us updated. And no i wouldn't of changed the fittings
Thanks for the replies. The owner has contacted the original installer. Will be interesting what they have to say. Probably end up sorting out for them. We will see. Were not all cowboys in Cornwall lol :)
If the house/owner is dodgy, our company would use red/blk cable and red tape etc.
No mate, never been there:D
Not disagreeing with any of the previous posts here, but, ......There are plenty of metal light fittings around that are manufactured to Class 2 requirements.
Reactions: 2 people
If no Rcd was fitted,the chances are the installer was a potcher who knows "a lot about electrics"
Nothing new in that,except these days he may be signed up as competent
Very true, but in a deathtrap like that common sense and risk management says just walk away. I wouldn't have fitted anything there. Problem being, what you do may not have made the situation any worse, but when someone gets electrocuted the name of the last person who worked on it is you so guess who ends up in the dock.
My question would be, is one under a duty of care to notify Building Control about it? If so, moral or statutory duty?
no RCD on a TT is an instant 2....so you wouldn`t be carrying out any work until adequate fault protection was in place...would you.
this could take the form of 100mA s type mainswitch with 30mA RCDs for the finals coupled with decent TT earthing arrangements (deep rod/s) for good, stable values of Ra..
just out of interest what was the Zs on the circuits in question?
Metal light fittings.
midgetman,
Badged01,