Hi Guys

Just some advice required. I understand meter tails ideally at 3m from meter but is it possible to have meter tails 10-15m from the meter?

Came across a job where there's no real option but to have the consumer unit 10-15m from meter cut out.

If it is possible is additional protection required at meter?

Thanks
 
The usual approach to satisfy everyone is to put the tails cable in as protected (typically using 3 core 25mm SWA, or usual singles in trunking) and feed it from a switched-fuse.

That way you can isolate the long cables as part of the "installation", and the fuse is under your control and (hopefully) chosen to be adequate for 5s disconnection for the end-of-tails Zs value.
 
I have a same problem where tails are in a cavity but customer needs consumer moving up the wall where I can not put in swa cable has space in the DNO cabinit where most metel fuse spurs are to big to go in.
 
It is one of those things that technically the DNO fuse might be enough (depending on Zs) for fault & overload protection so only an isolation switch is needed, but you ought to get the DNO's agreement on that. Hmmm...
 
  • Like
Reactions: buzzlightyear
The usual approach to satisfy everyone is to put the tails cable in as protected (typically using 3 core 25mm SWA, or usual singles in trunking) and feed it from a switched-fuse.

That way you can isolate the long cables as part of the "installation", and the fuse is under your control and (hopefully) chosen to be adequate for 5s disconnection for the end-of-tails Zs value.
Would the switched fuse be local to the meter or 10-15m away local to the consumer unit? Thanks for your reply
 
Would the switched fuse be local to the meter or 10-15m away local to the consumer unit? Thanks for your reply
Meter.
 
  • Like
  • Agree
Reactions: DPG and pc1966
At the meter, always at the source end of any feed (just like a sub-main).
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
liverpool

Thread Information

Title
Meter tails over 3m
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
adsmith,
Last reply from
adsmith,
Replies
7
Views
1,867

Advert