Just out on site it's very cold, wet haven't got regs with me. Just looking for some help. That's all.
 
Just out on site it's very cold, wet haven't got regs with me. Just looking for some help. That's all.

Feel a bit sorry for him now :sad3: Good on you Wirepuller!
 
  • Like
Reactions: 2 people
  • Like
Reactions: 1 person
Wherever he is, he shouldn't need to look in regs to find the minimum IR values. It's not exactly difficult to remember is it?
 
  • Like
Reactions: 1 person
The OP asks about a particular cable, I wonder if this is significant? The IR for the cable itself will be as per the manufacturer's info and will be inversely propotional to length, given in the form x megohm.km i.e. divide the figure by the length in km to get minimum value in megohms. But for a circuit, including the fittings at both ends and an unspecified length of the cable, as stated above.
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Well this was 2 hours ago. I hope he's in a warm pub by now worrying about what his highest resistance to alcohol is!
 
  • Like
Reactions: 2 people
The OP has not stated whether or not this is in an industrial setting,or how old the cable is. Some types of cable,in this instance,would have a calculated IR value far below what is stated in any "modern" regs book...and if a previously redundant cable was being brought back into service,monitoring would ensue,to check for a probable rise in IR value.

...1Meg...i hang awake at night,dreaming of 1Meg...:wacko:
 
Good evening gents.

Thanks for the helpful advice where given. Warm and dry now. Sorry for the lack of info. It was motorway spec cable. 150Ohms/L is the minimum. Was not thinking straight due to the frost bite setting in but knew it was there abouts.

Think sometimes to often when a question is asked on here the answer is look at the regs. Sometimes you need a little help in a shtt situation.

Cheers
 
  • Like
Reactions: 1 person
1 meg is a wonderful 'one size fits all' solution which makes no allowance for any real world factors which may apply to older cables or equipment.
It seems a bit ridiculous to me that a brand new installation only needs to meet this 1meg requirement the same as any old installation is judged by the same standard.
There is an old formula which can be used to relate the minimum value to the individual situation. The insulation resistance should be sufficient to ensure that the earth leakage current is no more than 1/10000th of flc
 
The original question asked what the minimum IR value for a 230v cable is as a regs book wasn't to hand, that implies the OP required the minimum value stated in bs 7671...which is 1 megohm!
 
  • Like
Reactions: 1 person
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Minimum IR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
mat155,
Last reply from
mat155,
Replies
23
Views
2,554

Advert