Dale.h

Main incomming supply is protected by a 60 amp main fuse
6mm Main/earth Bonding

6-way cartridge Fuse DB protected by 60amps main switch

Circuit 1- 5amp - Upstairs Lighting
Circuit 2- 5amp - Downstairs Lighting
circuit 3- 15amp- Immersion Heater
Circuit 4- 30amp - Ring main Wired in 2.5mm , Cooker/hob protected by 2 seperate unswitched fused spurs which are protect by a switched fused spur. (someone has obviously added to the ring main and place appreiate protection.)
Circuit 5-30amp - Ring Main in 2.5mm , Boiler
Circuit 6-30amp - Electric Shower protected by Rcd trip switch located in the loft , 6mm t+e


i should be able to seperate the cooker/hob supply from the ring main and place on its own breaker
main earth and bonding needs to be upgraded

the only problem im having is il have to install a 12 way board , but will the electricity board come and upgrade the supply to 100amps and the main tails and how much do they tend to charge??

apparently they installed a digital metre a few years ago but never upgraded the supply.

just need some advice really , maybe some more experianced members out there could shed some light.
 
a 10 way board should be adequate. looking at your loads, i don't think there's much chance of having sufficient load on at any one time to blow a 60A suppliers fuse.
 
a 10 way board should be adequate. looking at your loads, i don't think there's much chance of having sufficient load on at any one time to blow a 60A suppliers fuse.

Are you sure a 60amp is adequate , because i dont want to install the fuseboard and make the changes for it to blow the main fuse a week down the line..
 
If all the circuits are existing and you are not adding anything, there shouldn't be a problem seeing as it has survived before the new DB install
 
Are you sure a 60amp is adequate , because i dont want to install the fuseboard and make the changes for it to blow the main fuse a week down the line..

Given that your maximum load will possibly be when dinners on,the shower is in use, and the kids are watching the telly whilst the immersion is busy topping up the water temperature,if these were on for that "week down the line",there could be a possibility of --- no I changed my mind There should be an intact 60 amp fuse on the 8th day
icon7.png
 
if you check in bs7671. time /current graphs, you will see that a BS1361, 60A will stand 100A for quite some time without blowing.
 
and IR test between them neutrals n all.......classic `borrowed neutral` territory is this.....
 
in fact i would be IR testing the lot here first.....there may be stuff thats low....and needs replacing....
 
you`l need to get the Ze and PFC n all at the origin of supply......it could affect the max. withstand of the MCB`s you choose.....
 
and make sure you've got an adequate supply of smokes. best fault finding aid i've ever had.
 
  • Like
Reactions: 2 people
and make sure you've got an adequate supply of smokes. best fault finding aid i've ever had.

I don't smoke tel. I have a very clear vision of that bottle of red wine in my mind, just waiting for my attention later....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Need Advice on Fuseboard Upgrade!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Dale.h,
Last reply from
Guitarist,
Replies
12
Views
2,249

Advert