I have 3 double sockets all fed from separate 32 AMP EACH . The distance is 2m from the board and the cable is in 25mm metal conduit.
I have used 4mm single core cable for each socket . I’m told I need to upgrade this to 6mm single core . Why is 4mm not big enough ??

(reason it’s single is so each socket is independent due to what gets used in them CANT have all appliances off at once,just incase or I would have a ring)
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
Why am I being told it need upgrade to 6mm ?
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
I’m told the table says MAX is 30 for 4mm in conduit . Cause it’s a 32 then 6mm Is needed . Is this right
 
Does that post about 4mm in condguit in table says 30 max help explain
He says the table for cable says max is 30amp ( obv there is a 32amp breaker which will never be reached ) so 6mm is needed . Where can I find this table independently so I can see for myself
 
This is Table 4D1A of BS7671.
20220506_151319.jpg
 

Reply to Need some advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
935
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi everyone. Im new here... I need advice on wether it is safe and okay to have 3 × 13amp fcus on its own radial with each having single socket...
Replies
22
Views
3K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock