I have 3 double sockets all fed from separate 32 AMP EACH . The distance is 2m from the board and the cable is in 25mm metal conduit.
I have used 4mm single core cable for each socket . I’m told I need to upgrade this to 6mm single core . Why is 4mm not big enough ??
(reason it’s single is so each socket is independent due to what gets used in them CANT have all appliances off at once,just incase or I would have a ring)
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
Why am I being told it need upgrade to 6mm ?
I’m told the table says MAX is 30 for 4mm in conduit . Cause it’s a 32 then 6mm Is needed . Is this right
Does that post about 4mm in condguit in table says 30 max help explain
He says the table for cable says max is 30amp ( obv there is a 32amp breaker which will never be reached ) so 6mm is needed . Where can I find this table independently so I can see for myself
This is Table 4D1A of BS7671.
Reply to Need some advice please in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
4K
Hi everyone. Im new here... I need advice on wether it is safe and okay to have 3 × 13amp fcus on its own radial with each having single socket...
Hi, I am Currently in the process of building an extension and my builders will shortly be getting their electricians to commence the first fix...