Discuss New caravan site in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

E

eddiecme

Hi All,

I've got a job to do at new caravan site. The client is paying for 3phase off of the pole that runs through the field and they have built a small solid building at the base. I'm assuming it's going to be connected as PME but i'm yet to confirm.
The client wants supplies to 5 pitches for mobile (drive in) caravans. A little shed type thing for each pitch is going to be installed with a 16A hook up socket and 13A double socket running from a small d/b in each shed. There will also be a 3phase supply to the bore hole pumping station, and single phase supplies to an external pump, electric gate and two further out buildings.
He wants all caravan supplies metered at the main d/b, i've priced a Hager board with internal single phase KW/hr meters, running SWA supplies in the ground to the 5 individual pitches. When two further 16A circuits in each shed for the two individual sockets.
I've never worked on a new caravan site but had a good read of GN7 so just want a few questions answered/opinions on how people would do this with regards to RCD protection and earthing. If it is PME i was thinking running MCBs from the main d/b to supply the sub boards which would have 16A 30mA RCBOs inside, and an earth rod connected to each sub board segregating the PME.
Also opinions on upfront surge protection and options for installing non flammable but still IP rated d/b's in these locations would be appreciated.
Eddie
 
What on earth has non-flammable DBs got to do with caravan sites?

I would be looking at making the whole site a TT as from your description there doesn't appear to be anything which would benefit from a PME earth. With a bit of consideration you could get a very good Ra on such a site with plenty of rods linked together.
 
What on earth has non-flammable DBs got to do with caravan sites?

Absolutely nothing to do with it, ffs its been a long day!


All supplies would then need further RCD protection at source, i guess would be the only implication but you're right i could stand to have a fair few rods in the ground.
 
Absolutely nothing to do with it, ffs its been a long day!


All supplies would then need further RCD protection at source, i guess would be the only implication but you're right i could stand to have a fair few rods in the ground.

If you get the earthing right you likely won't need additional RCDs at source.
 
what i've done on similar installs is to use the pme for fault protection of the SWA feeder cables to each pitch, but isolate the earthing at the pitches and TT each pitch.
 
what i've done on similar installs is to use the pme for fault protection of the SWA feeder cables to each pitch, but isolate the earthing at the pitches and TT each pitch.

i think this is what i'm probably going to go for. What SPDs have you installed previously?
 
SPDs? For what part?

I've often installed similar to as telectrix describes.

ESQCR prohibit PME earthing facilities on the pitch socket, so I would distribute PME, isolate the earth (and label it not to be connected) then TT at each point, then something like a 25A/30mA 61009 per pitch. If there is plan for power to the shed for lighting and socket-outlets as well then a little board should suffice.

You could convert to TT and then distribute, but you may have discrimination issues with the RCD and the supply end popping.

It'll be a nice job if the sun is out.
 

Reply to New caravan site in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
869
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
557
There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Replies
0
Views
880
Hello, not sure if this is allowed but here goes, I was recently staying on a caravan park along with many others, (touring caravan not static)...
Replies
6
Views
2K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock