I am busy doing a rewire on a property, really old electrics, old rewireable fuses, NO earth. Main earth cable was enclosed around a screw on the cut out fuse.
Who is responsible to sort it out?
I have contacted UK power network, they always say they are going to send someone out to assess the problem, and see if there is PME available in the street?
If there is no PME available, they say i have to install an earth electrode. Surely they can peel the sheath back the distributors cable and attach an earth clamp?
They say the electrician is responsible to provide an earth path, but surely it the distributor who is providing power.
Could anyone please give me some more insight, as its not the first time
Thanks in advance
I think it may be down to you, I believe they only maintain an earth if they supply one. Obviously they're not supplying one.
May have to try for a PME upgrade (which will cost).
The DNO will only maintain an earth facility which they provide, if it's not there they will give you a choice of either paying an exorbitant amount for a PME or sinking earth rods
I think you will need to install a earth rod as has beed said the DNO only need to maintain the earth if they supply one.
You're missing something mate, there could be any one of a few reasons why they didn't supply an earth. For one, PME wasn't available at the time.
not always the case,I believe that if they supplied an earth originally then they must maintain it however if they did not then the have no legal obligation to supply one,many years ago it was down to the sparky to provide an earth and this would be tested by dno before they would connect supply.
That's where the earth rods come in Farm, TT systems all have individual earth electrodes. I and my wife, kids and dog have been living in one of these places for 20+years with no ill effects whatsoever. When I rewired I got an Ra/Ze of 1 ohm so I'm pretty confident it's fit for purpose
- - - Updated - - -
So they used to just supply phase and neutral to properties what year did this stop or what age of properties would this accur in
They still do it to this day
Indeed they do Trev, especially if fed from overhead,mind you I remember when i was a kid in the early 70,s and we had a new house on an estate and that was TT.as you say still pretty common.
DNO can only maintain an exhisting earth if its reported to them as a danger! if theres no chance of of a pme, you have to put a rod in the ground
So they leave a property with no earth facility dosnt sound safe to me wouldn't live there with my family
Older installations were safe.
You had to provide a good earth by whichever method you found suitable, which the DNO tested before they made the final connection.
The earth was quite often thro' the lead water pipe and was a good earth.
Water boards used to allow the supply of water thro lead pipes, they wouldn't nowadays as things have moved on.
Same with electrical earthing.
Lead cables buried in a wall were never a hazard.
Since the use of plastics for outer insulation and for gas and water supplies, earthing has become far more important.
If there is an earth connection there, provided by the DNO, then you have an earth connection, ...it just hasn't been distributed. Where is this earth cable coming from and have you tested this earth connection (Ze) ?? Only after testing, can you determine whether you have a functional earth connection....
I don't know why everyone here is saying, that you ''HAVE'' to pay for PME earth connection. I know that some unscrupulous DNO's have made PME connections chargeable, but most to my knowledge don't charge where a PME connection is already available!!!
Reply to No earth on installation, WHO is responsible??? in the UK Electrical Forum area at ElectriciansForums.net
I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking...
So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...