Discuss no water bond, code query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

graham123

Doing a periodic at a primary school and am unable to locate where the mains water is isolated from, the earth bar doesnt account for a bond to the water as ive found where all the other go. Ive been told in the past no bond is a 1, but in this case i cant find where it is isolated so a 2 or 3? opinions welcomed
 
If you can't find the connection for the water bonding then do a continuity test from MET to the furthest part of the water system to see if there is bonding in place. If there is apparently bonding in place then it is 3 requires further investigation (though really this should be found at the time). If there is no indication of bonding in place then this would I think be a 2 as there is the potential for danger in the case of a fault.
 
If you can't find the connection for the water bonding then do a continuity test from MET to the furthest part of the water system to see if there is bonding in place. If there is apparently bonding in place then it is 3 requires further investigation (though really this should be found at the time). If there is no indication of bonding in place then this would I think be a 2 as there is the potential for danger in the case of a fault.

'Fraid I dont entirely agree with the test method. It is not the furthest point of the water system that requires bonding,it is the nearest. Parallel paths through conductive parts in contact with the water system will give false results. And it is because the system may be at the potential of the general mass of earth that it needs bonding at the point of entry....if it is at earth potential...you are liable to get a misleading continuity reading to the MET whether it is bonded or not.
The point of entry needs to be found,from there you can establish whether or not the water is an extraneous conductive part. If it cant be located you should assume it is not bonded and apply a code 2,as Richard states...perhaps with an explanation such as. "Unable to locate incoming water supply and associated main bonding,requires improvement"
 
Last edited by a moderator:
'Fraid I dont entirely agree with the test method. It is not the furthest point of the water system that requires bonding,it is the nearest. Parallel paths through conductive parts in contact with the water system will give false results. And it is because the system may be at the potential of the general mass of earth that it needs bonding at the point of entry....if it is at earth potential...you are liable to get a misleading continuity reading to the MET whether it is bonded or not.
The point of entry needs to be found,from there you can establish whether or not the water is an extraneous conductive part. If it cant be located you should assume it is not bonded and apply a code 2,as Richard states...perhaps with an explanation such as. "Unable to locate incoming water supply and associated main bonding,requires improvement"

Yes, this is a better description, I was probably being a little simplistic.
If the point of entry cannot be found then it is not possible to determine correctly if the water is bonded so a code is required of some sort.

I was working on the principle that if you have a continuity check of say 0.01 ohm at a distant part of the water pipework then the consideration may be that the water pipework is in effect bonded (though possibly not correctly bonded, as evidenced by the lack of the conductor at the MET) and would be unlikely to cause a danger in case of a fault so a code 3 may be appropriate.
If you get say 4 ohm then this is not effectively bonded and would need a code 2.

However this "method" is not an approved or regulated means of determining correct bonding and as you say could well be a misleading reading.
Explanations on the form are always good (wish I had thought to put that!)
 
i have to agrre with you richard i have been unable to find the water bonding i then test here and there and if i get a good reading i'd code it as a 3
 
I would not put this as a code 3.
If you cannot find the connection, but believe there is one, then it must be inaccessible, which could be either code 2 or 4 depending upon how dangerous you believe having an inaccessible connection is. It would warrent being recorded as a LIM in any event, as there should be no other reason for you to be unable to find the connection.
 
On any report with my name signed, if I can't be sure of a bonding connection including sight of an appropriate clamp etc. then it's a code 2.

Why would you allow any discrepancy or ambiguity in your report?

There is no advantage to you as the inspector in recording this as a code 3 or 4.
 

Reply to no water bond, code query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
551
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top