c.boy

-
Reaction score
0
Howdi,

Changed a d/b on fri and carried out a full test on a top floor flat,3 storeys high. Most of my readings were pretty bang on appart from the p.f.c which was 7.1 ka my ze was 0.10.Doing the formula it should have been around 2.3 ka as if im correct pfc= 230/ze . Ichecked the reading 3 times and still 7.1 ka was the reading. My gaffer has phoned me today to tell me that this is an unacceptable result.without trying to find the main earth in the field outside how would i be able to get a better reading????? the system was tncs with a bs1361 type 2 which has a rated short circuit capacity of 33ka.yeah 7.1 is a bit high but surely its well within the capacity of the bs 1361????
 
hi
thanks for the response.
yeah true!!! all breakers are type b rcbos which is 10k and the type c are 6k (could be wrong tho) how would a be able to reduce the reading on the p.f.c tho??
 
Ze is measured with the earthing conductor disconnected from the bonding conductors to avoid parallel paths
PFC is measured with earthing conductor connected to bonding conductors etc so there will be a different loop impedance hence the difference between measured and calculated values.
If you read OSG page 88 It is not recommended that installation designs are based on the measured values of PFC as changes to the distribution network, subsequent to completion of the installation may increase fault levels.
OSG page 56 - for domestic single phase supplies up to 100A the PFC is unlikely to exceed 16.5 kA
con units incorporating protective devices complying as a whole assembly with BS 5486-13 or BSEN 60439-3 are suitable for fault currents up to 16kA when supplied through a type II fuse to BS 1361

DO NOT try to reduce the PFC reading it is high probably due to the sizes of pipework in the building and the steel frame contruction providing low resistance for fault currents.

I understand the OSG as explaining in domestic properties if the Fault current is high the Main fuse will blow before damage is done to MCB's
I agree it all sounds a bit confusing but your 6kA MCB's should be OK
If you are still not Happy then change MCB's to 10kA
 
hi thanks for your reply.

yeah a mentioned that to my gaffer!! but he said it was totally unacceptable!!! and stormed off!!!no explenations as per usual!!!all fuses are rcbos type b which are 10k a think pal???new to the testing not done it since ma trade test,seem to find all the older sparks get the honour!!!!! a did say because its a flat top floor readings may be higher but he wants everything bang on if you are .02 out on a zs he ???? it!!! maybe a should just start doing the formulas LOL!!!am the only one out o 12 guys who ???s this and really getting a bit ****ed off as its my name on on the cert, at the end o the day!!! but a am right in saying that without finding the supply earth a would never be able to sort this yes????
 
hi thanks for your reply.

yeah a mentioned that to my gaffer!! but he said it was totally unacceptable!!! and stormed off!!!no explenations as per usual!!!all fuses are rcbos type b which are 10k a think pal???new to the testing not done it since ma trade test,seem to find all the older sparks get the honour!!!!! a did say because its a flat top floor readings may be higher but he wants everything bang on if you are .02 out on a zs he ???? it!!! maybe a should just start doing the formulas LOL!!!am the only one out o 12 guys who ???s this and really getting a bit ****ed off as its my name on on the cert, at the end o the day!!! but a am right in saying that without finding the supply earth a would never be able to sort this yes????
Direct your boss to this site so we can give him a few lessons about his job, is he an armchair boss you know the penpushing type or does he do his fair share on site the place where you learn things lol:D.
 
armchair all the way!!!! does a couple o courses and knows everything!! never on the tools mind you the only way you get a gaffer job wi the council is that you cant work ont the tools!!! a wish a never left the petro chem industry!!!!!!!!!!!!!
 

Reply to p.f.c in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
hi, fitted new consumer in a domestic house. testing. ze 0.16 zs at origin 0.04 pfc 6.2ka the pfc is my problem, ohms law would make the pfc...
Replies
16
Views
7K
I have been asked to carry out a rewire of a top floor flat when checking the existing supply characteristics. TN-S with a ZE of 1.24 ohms and...
Replies
27
Views
5K
B
just installed cooker cct, rcd fuse box,earth bond main services etc. tested ze which was 0.02ohms and the pfc reading was 12.2 ka which i thought...
Replies
3
Views
9K
Working in a high rise block of flats bout just under half way up!! changed the c/u now my ze is 0.01 prob parralell paths,however my pfc is 19.9...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock