Discuss Partial rewire?? in the UK Electrical Forum area at ElectriciansForums.net
M
mstoker1990
Hi just wondered if someone could give me some advice I am currently in a property that has suffered fire damage. Nothing extensive but will need a new consumer unit and all wall and ceiling fittings replacing. Everything is around 15yrs old all looks ok. Bonding needs upgrading but the whole house is on one ring main how do I stand with this with the the regs? Is it a fail?? It is. 3bed semi. Would appreciate your advice. Cheers
a single RFC for the whole house is not a fail, as you call it. while not ideal, as long as the circuit is correctly protected, the only problem would be with MCB tripping if the circuit was overloaded.
edit: i would just add a note on the cert. that it would be advantageous to install a separate circuit for the kitchen.
Is it your house or a client?
If its yours and you do have to do a lot of remedial work, I would seriously consider changing the socket circuit so its 2 circuits rather than one, plus I'd be checking for a borrowed neutral on the landing light as a new dual rcd board may dictate additional cabling too.
It is a better class of install where there are multiple circuits for the connecting loads,but how big is the house ?
Unless its a rich mans monster then one ring should be fine if it tests Ok
It would be worthwhile making alteration to the set up as stated by the others
When you have fitted the new cons unit,if there were another ring ( kitchen is usually easier to alter),the user would not lose all the sockets when a rcd tripped
You say the whole house is badly fire damaged.
If they are going to gut the whole house then you might as well do re-wire on the whole house instead.
Explain the situation to the owners and ask them what they want to do.
I take this will be an insurance job so they will want to get as much as possible out of it.
If your quoting then do a quick EICR to justify why you want to do the whole house - easy to make it look like a short circuit - just join all cables together in CU
They will prob go with you then because you identified the problem and fixed it at the start instead f having to change your quote (or keeping same price and doing a cowboy job) if the problem araised later
a bit of overkill there, if most of the damage is just smoke damage to accessories, but a thorough test/inspect is needed so as not to under estimate.
Just thought to make the letters a little larger nicholas
:smile:
do you want to borrow mine?
Yes I was joking!
I was mainly on about if the tails where damaged then they would have to be replaced as well - and the circuit tails - still might as well have been easy to do a full rewire - you have to see how much damage the heat has caused. - could of lowered IR readings!
Cheers guys the fire has been in the living room and the only heat damaged item is the pendant in there the rest is all smoke damaged.
Putting a report in going to request to do a partial rewire upgrade bonding etc
Cheers
Have you IR Tested the circuit in that room?
Those rooms can get well over the 70C that the cables are rated for - any low readings need to be sorted - also do a continuity test to get your Zs reading (Zs = (R1+R2) + Ze
If you dont know Ze then take it as the highest allowed reading for the type of earthing
Also back your requests up with evidence why you want to do what your suggesting to do
and make sure you put in a good price. don't undervalue the work. the insurance company have probably received more in premiums over the years than the cost of the job anyway.
Reply to Partial rewire?? in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hello all, We've had a rewire and our electrican is currently away on holiday so we're unable to ask them for advice. Please can I ask for your...