jake2194

Good morning all,

I'm new to this forum and just wanted some advice please.

I've got this electrical ball pump that PE use which is a class 2 appliance, last year it passed the PAT test but this year it failed on the leakage test. Now I could do a class 2 test without a leakage test but I don't normally do these as I always normally do a class 2 soft test with a leakage limit. Just wanted to know if I should tell the PE team it failed and they have to get rid of it or if I can do the other class 2 test without a leakage test.

Any thoughts on this would be much appreciated.

Cheers,

Jake
 
Welcome to the forum!

The point of PAT is to determine whether equipment remains safe to use; avoiding a test that something is expected to fail is cheating. Sometimes it is problematic to do a leakage test and one might need to omit it, but anything capable of being tested should be tested and must pass. If last year it passed a test that it now fails, it has probably deteriorated in some way that makes it dangerous or more likely to become dangerous.

I can't imagine it would be very expensive to replace but the point here is getting a clear picture of deterioration modes or possible testing inconsistencies. What type of leakage test are you doing and what is the leakage current reading? Is it possible that a different type of test was done last year and that is why the result is different, not because the pump has deteriorated? E.g. a substitute leakage test vs. a full voltage one?
 
  • Like
Reactions: DPG
A leakage test is generally only carried out if the insulation resistance tests gives suspect results or for some reason an insulation resistance test cannot be carried out. It is generally not deemed a prescribed test.
 
  • Like
Reactions: Lucien Nunes
OK, good point. I am used to working with stuff that has high leakage and internal VDRs that spoil insulation tests, so in our industry the leakage test is pretty much unavoidable.

But the concept is still valid that if something passed a test and now fails the same test, there is reason to think that the test might have found a problem.
 
  • Like
Reactions: westward10
I wouldn't be surprised if whoever tested it last year didn't do the leakage test.
 
  • Agree
Reactions: Lucien Nunes

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PAT Testing a ball pump
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
jake2194,
Last reply from
DPG,
Replies
4
Views
1,514

Advert