Nicktric

Hi I am confused with my readings for Pefc as my Ze is .09 which would give me 2.55Ka but when I test PFC on my meter I get 5.62Ka? Ze, Neutral and earth leads clipped on disconnected main earth, probe Line on Supply side?

Can I check I am doing this correctly;3 lead PEFC piggy back Neutral/Earth clip on MET test on supply side of RCD. Pscc Clip on MET earth lead probe Line and probe Neutral supply side RCD?
Thanks
 
The Ze should be measured with bonding disconnected, PFC with bonding connected to get a worst case scenario, this normally means that measured PFC is higher than V/Ze.
 
as IQ's post. parallel paths will give you a higher value when measured than you would expect from the Ze reading. out of interest, you could re measure Ze with all the bonding and earthing connected, then re calculate PFC. ( not for the records, just to prove a point )
 
true, but if his measured pfc is a lot higher than calculated, must be so.
 
HI, CAN SOMEONE HELP ME ON THE PROCESS FOR TESTING Ze,
Q: isolate the supply,disconnect the main earthing conducter (MET),put the earth lead on the disconnected earth and the neutral on the supply side,and the live and the supply side,then test, and record the value? (am using a fluke 1653b)
 
Last edited by a moderator:

Reply to PFC Calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
553
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
911
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock