john h owen

when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?
 
when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?

First of all, short circuit = L-N. Earth fault = L-E. You're on the right track though, take the highest PFC and double it.
 
when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?

Personally on a 3 phase i only test between phases for PFC as it has to be the highest and don't worry about the L - E & L - N single phase readings.
 
Same here. My meter can test directly between phases. However if I was using a meter that couldn't then I would just test each phase to neutral and double the highest result. I ignore PEFC as PSCC must be higher in a three-phase system.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
pfc on 3 phases
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
john h owen,
Last reply from
Risteard,
Replies
3
Views
7,219

Advert