john h owen

when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?
 
when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?

First of all, short circuit = L-N. Earth fault = L-E. You're on the right track though, take the highest PFC and double it.
 
when prospective fault testing a three phase circuit do you only need to do the short circuit test only on the 3 phases in turn due to result being twice that of the earth short circuit current due to the line voltage being twice the value?

Personally on a 3 phase i only test between phases for PFC as it has to be the highest and don't worry about the L - E & L - N single phase readings.
 
Same here. My meter can test directly between phases. However if I was using a meter that couldn't then I would just test each phase to neutral and double the highest result. I ignore PEFC as PSCC must be higher in a three-phase system.
 

Reply to pfc on 3 phases in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
363
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
661
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
853
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
491

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock