can anyone tell me the stated difference between prospective short circuit current and a prospective earth fault current test
cheers certa
cheers certa

pssc is the max current that can flow between Line & Neutral.
pefc max current flow between line earth.
If TNC-S using ohms law they will be the same.
Prospective Fault Current is not the same as Prospective Earth Fault Current. PFC is the greatest of the PEFC and the PSCC.