M

mick1974

I know you should put all three phases and neutral through the same opening of enclosures and not split them(two in one hole and one and neutral in other).
But i can't find the regulation for this.
 
as marvo says. it's only with ferrous enclosures that you may get eddy currents. thanks for reminding me. eddy owes me a tenner from a bet.
 
ah, like market and meerkat. sssimplesss.
 
Yep- 521.5.1 Ferromagnetic enclosures: electromagnetic effects
The conductors of an a.c. circuit installed in a ferromagnetic enclosure shall be arranged so that all line conductors and the neutral conductor, if any, and the appropriate protective conductor are contained within the same enclosure.
Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferromagnetic material.
 
Only in metal (ferrous) enclosures

That's not actually a correct statement!! Drive enough current through an alluminium plate and you will still see circulating currents being produced, not as pronounced as in a ferrous metal situation, but depending on current flow, can still reach detrimental levels!! I always replace all switchboards alluminium gland plates with paxoline (or equivalent) gland boards. Many of our switchboards will be seeing potential loadings approaching 2.5 to 3.2 KA through incoming parallel single core cables!!
 
I know you should put all three phases and neutral through the same opening of enclosures and not split them(two in one hole and one and neutral in other).
But i can't find the regulation for this.

Its in part 5, but i cant remember the reg either, and it is worded in the usual garb, so not so easy to dig out.
 

Reply to phases through separate openings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
288
We have to install 3 x 240mm singles and 1 neutral to a panel in a LV room.the ducts aren't large enought.What happens if the singles are split...
Replies
9
Views
431
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
577
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
457

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock