40 amp mcb, 10mm 3 core swa, garage Cu, would cover most garage supplies and allow for future upgrades.

If there really is the likelihood of say an Ev point or hot tub, then I would use an SP+N fused connection unit.

But like already said, more information is needed.
 
Last edited:
Cheers for the replies, much appreciated.

So the db is in the porch on the ground floor (highlighted red) and the first floor pic with red lines is my proposed route going under the floor boards or up into the loft.
 

Attachments

  • Screenshot_20230620_184955_Rightmove.jpg
    141.8 KB · Views: 15
  • Screenshot_20230620_184949_Rightmove.jpg
    128.7 KB · Views: 20
I will run the T&E down the wall.either from the loft or from under the floor on the first floor (half way down) into a joint box with the swa which will go to the garage
 

Attachments

  • 20230620_184650.jpg
    194.1 KB · Views: 19
The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
 
Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
 
Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
Well I was thinking twin and earth (e.g. 6mm) would be cheaper and easier to run under floor boards etc.

Tbf I could use that blank space for a 40A MCB to supply the garage couldn't I 👀
 

Reply to Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
736
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
562
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
This is a question with probably so many answers and solutions, but I wondered how people would do it. I have a clients house which already has...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock