My pool pump (230V 1Ph cap start) US Motor k63cxdfw-5159 ) wasn't working so I started to look for a reason. I found the terminal to the output control relay in the Intermatic program timer/ freeze control was burned off. None of the terminals were insulated and very close to each other and found a skeleton of tiny lizard in the wiring area. So I figured the lizard shorted the terminals together. I removed the output wires and tested the relay and got 230 across the DPST contacts as expected so I knew the relay was good. I replaced the terminal with a fully insulated flag, reconnected the wires thinking that would fix it. But when the timer turned the pump on, the motor sparked and smoked and tripped the breaker. I took a Ohm reading on the motor and read .06 ohms between the L1 and L2, and 1.61 ohms between L1 and ground, and 1.61 ohms between L2 and ground. Do these reading indicate the problem? What other tests can I do to the motor and wiring to fix the problem? Thank you in advance for your educated opinion.