D
darren
Hi Guys.
Got a job coming up where the customer wants me to install power to two portakabins. I have a few questions and would really appreciate it if someone could help out.
They are located on a waste recycling site and will be used as the sites offices the previous cabins that they are replacing have been there for 6+ years.
The cabins are going to be placed one on top of the other strapped together with metal bracing bolted to the ground and cabins with metal stairs going to the top cabin.
If i was to assume I'm treating it as permanent fixture and a tn-s supply can anybody see a problem with running out a 16mm 3 core sub main and using the spare 16mm as the earth or should i make it TT? (main supply is less then 5M away from cabins)
Not 100% sure on what the supply is so say its tn-c-s could i again continue the earth or would i have to TT it?
Both units will have a separate feeds and will be fed from a 3 phase dis board, if possible i would like to avoid the TT approach seeing as the area is concrete heaven strong enough to withstand the hammering of 25+ ton trucks 24*7 with soft ground nowhere to be seen!
Thanks in advanced
Darren
if I'm talking bs let me know, i have recently qualified and every time i think i have learned something it turns out that there is always more to it
Got a job coming up where the customer wants me to install power to two portakabins. I have a few questions and would really appreciate it if someone could help out.
They are located on a waste recycling site and will be used as the sites offices the previous cabins that they are replacing have been there for 6+ years.
The cabins are going to be placed one on top of the other strapped together with metal bracing bolted to the ground and cabins with metal stairs going to the top cabin.
If i was to assume I'm treating it as permanent fixture and a tn-s supply can anybody see a problem with running out a 16mm 3 core sub main and using the spare 16mm as the earth or should i make it TT? (main supply is less then 5M away from cabins)
Not 100% sure on what the supply is so say its tn-c-s could i again continue the earth or would i have to TT it?
Both units will have a separate feeds and will be fed from a 3 phase dis board, if possible i would like to avoid the TT approach seeing as the area is concrete heaven strong enough to withstand the hammering of 25+ ton trucks 24*7 with soft ground nowhere to be seen!
Thanks in advanced
Darren
if I'm talking bs let me know, i have recently qualified and every time i think i have learned something it turns out that there is always more to it