R
R1CH-G
After a couple of days of intensive cable calcs, diversity, max demand, etc. etc. etc. I have finally managed to disappear up my own jacksie! My head is officially in bits and for the life of me, I cannot get my box round one simple thing.
If a 3 line motor is rated at 60 amps, what is the line current?
I've oficially lost the will to live and going to have a kip in a bucket of homebrew ;)
is it 60A total? what's the kW rating or HP?
Upvote 0
Not been given kW rating or HP, just that it's a 60A motor. It's a course question on my 2391-20 ~ I don't think this bodes well for the final outcome not being able to work this out :o
Upvote 0
I don't think you have been given enough info and in my limited experience motors are rated in HP or W for output or VA for input, but then you would have to know the efficiency. Also i would have expected to have been given a power factor :confused:
Only equation i can think of is IL = P/(√3*VL*PF) but you do not have know enough for that.
If the 60A was a phase current (Ip) then you would need to know if the motor was connected in star or delta.
Be interested to know if you get an answer?
Upvote 0
Yes, if I had the information to fit it into that formula, there would have been no problem. So probably not a surprise that I was getting nowhere in a hurry.
I think I may have to reverse answer the question, and make a few assumptions!
Thanks for the feedback.
Upvote 0
depends which bit of her you want to kiss
Upvote 0
ok the way i read it is with the info given:
star eqn is: IL = IP therefore VL = sqrt 3 x VP therefore transposing gives VP = VL / sqrt 3
IL = 60A then IP = 60A 60A if star
Delta VL = VP therefore IL = sqrt 3 x IP therefore transposing gives IP = IL / sqrt 3
so IL = 60A / sqrt 3 = 34.64A if delta
thats how i read the question anyhow, so hope it has not added to the confusion?
Upvote 0
P
K
Probably a Dumb Question, BUT
Electrician Courses : Electrical Quals
Thread Tags
R1CH-G,
ukpablo,
Electrical Courses