Agree. No problem with 30mA RCD protection to AC cable if embedded in wall <50mm to comply with regs.

It is wrong to terminate the CPC through the isolator terminals rather than the fixed terminal which I suspect you will see in the rear of the isolator enclosure.

And even more disappointing the original installer hasn't offered his service to arrange a de-energise and recommission after the works have been conducted. Good customer after care/service is the seed to good business. But may be he knows whats wrong.
 
Where's the Isolators for this inverter?
Twin and earth for DC into inverter? I might be wrong with this but I'm sure T&E is not allowed for DC with PV systems, >120v has to be double insulated , or maybe you can if its fused ?
Warning labels, schematics, shutdown procedure etc?

hope that installer is using this for his next Mcs visit!
 
if that inverter is outside i would be just as worried as the lack of everything else! That housing isn't rated for outdoor use
 
I was surprised at the "electrical install" side of it. I am putting the supply cable through the RCD, its my signature at the end of the cert and I shall also be writing a covering letter just to make sure my backside is not exposed......so to speak
 
If I were you I would move that inverter in side lable it up correctly use isolator. Also you won't be able to use an rcbo they don't work correctly eith current flowing the wrong way through then it will need to be an mcb with a rcd main switch
 

Reply to PV system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
837
Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
725
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
849

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock