If you did a PIR for a 2391 exam and after testing found insulation resistance on a circuit to be 0.4M Ohms between line and earth on an outside light which code would you use?
Would you use code 2, requires improvement or code 3 requires further investigation?
I used code 3 and got the wrong answer according to this mock test I am doing.


Also if you found the breaking capacity of the fuses to be below the PFC would you code 1 or code 2 it?

Thanks alot.
 
Last edited:
the first part could be a 2 or a 3 IMO. the second part i would code 2. as requires improvement, but no immediate danger.
 
The other codes were to do with not having RCD protection in the offices, Code 4.
Now I thought offices were full of skilled and instructed persons.
I guess if the question does not mention they are skilled and instructed then you have to assume that they are not.
Also the work shop ring had no RCD protection code 4.
I thought work shops were full of skilled and instructed persons and the only time you would need RCD protection was if you had a socket that could be used for mobile equipment outdoors.
I wonder how flexible City and Guilds are with their answers to coding questions.
 
Last edited:
That IR question is a little teaser. If you read Reg 612.3.2 it states

" The insulation resistance measured with the test voltages indicated in Table 61 shall be considered Satisfactory if the main switchboard and each distribution circuit tested separately, with all it's final circuits connected but with current-using equipment disconnected, has an insulation resistance not less than the appropriate value given in Table 61"

So as your reading was 0.4 Mohm it can not be seen as satisfactory and yes a code 2.
 
Last edited:
Zs reading above max. allowed. boxed in BS951 clamp on water or gas so you can't actually see that it's connected. anything that you think requires further investigation to determine if it's satisfactory or not.
 
Tough one, I read it out the book and am not sure myself.

I guess if he is in the car park testing an outside light and notices the car park lights that are not part of the inspection are falling apart with wires hanging out of them all over the place.
 
"The person ordering the report should be advised that the inspection has revealed an apparent deficiency which could not, due to the agreed extent or limitations, be fully investigated"
 

Reply to Quick couple of coding questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
901
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock