Discuss quick test on a garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
J
jimmylaud
new to this so just looking for a bit advice and to see your thoughts had a quick test on a garage todayjust to check condition of wiring results i got were.
Tnc-s supply 6mm armour out to feed main board in garage
sockets zs- 0.56
R1-0.32
rn-0.32
R2-0.48
R1+R2-0.48
Insulation
L-N 82.6M
L-E 70.6M
N-E 0M
now my questions i thought R1,R2 was meant to be a quarter of R1+R2?
on the insulation test did i get a dead short due to earth and neutral having the same potential?
any help would be great
R1 + R2 = (r1 + r2) / 4.
As for insulation resistance, how do you know it's a dead short?
0 million ohms isn't necessarily the same thing as 0 ohms.
thanks for the reply so saying that R1+R2 should be 0.2 going with my results am i correct there?
as for the insulation i just tested N-E at 250v and it said 0.00 M ohms thanks again in advance
yep, R1+ R2 should be 0.2 and as for the insulation resistance, i would imagine there is a short, probably a socket pin through the neutral, is it not RCD protected?
hi its tn-s in the house, no the cables were not discotted at the garage cu:eek: didnt realise you had to do that, what are your thoughts on the R1+R2 thanks again
If you tested the distribution board/installation as a whole then you need to disconnect the neutral/earth link for a TN system. Low Voltage systems should be tested at 500V d.c. (ELV 250V d.c.)
Yes, I make it 0.2 ohms as an expected approximate value for R1+R2.
when you say your IR was 0ohms, where were u testing?
dont worry about asking questions, my mate stuck 500v across a 3ph board full of rcbo's and at the load side of a fire panel?
R1-0.32
rn-0.32
R2-0.48
R1+R2-0.48
Well the calculation on a ring would work out at (r1+r2)/4, but if you have done the figure of 8 test then this could have been due to spurs. If the figure of 8 test was conducted the other way around, you could get spurious results.
The live neutral fault could be due to the main switch not being open. If this is the case, then you would be seeing the neutral-earth link the PME head if it's TN-C-S, or back at the star point of the transformer if it's TN-S.
Make sure you've isolated from the main switch, and left all MCB's on and fuses in place.... :)
for anyone like me who didnt know what spurious was:eek:
–adjective1.not genuine, authentic, or true; not from the claimed, pretended, or proper source; counterfeit.
Just pointed this out to the missus, and she doesn't know what it means either... So you're not alone!!
That'll teach me for reading the "improve your word power" section of Readers Digest in the bog for the last 25 years or so, :D
thanks for all the replys so basically what i should have done was disconnected the ring from the board and then done the insulation tests? What do you mean by figure of 8 test pevvers? Has anyone got any thoughts on why my R1+R2 was higher than it should be thanks again
the R1+R2, if all sockets was on the ring,you would expect to be about 0.2 but if there was a spur off the ring then that would be added which would give a higher reading
as for the insulation resistance, if you are testing 1 circuit only, you must disconnect it, (L,N+E) and of course disconnect/unplug any appliances and remove any bulbs etc, but i find it is a good idea to test at 250v, to make sure nothing is still connected, before doing 500v
Reply to quick test on a garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...