Interested to hear how different people approach doing loading / vd calcs for larger size single core cables in a 3ph situation - ie 3 separate L1, L2, L3 & N cores above say 95mm.
 
For cables that have 3 figures: r (resistive) x (reactive) z (impedence). I use the z value for mV/A/m as a general rule of thumb.
 
  • Agree
Reactions: pc1966
Unless you have figures for the supply Z (e.g. transformer, etc) decomposed in to R & X, etc, and it is comparable to the cable figures then simply using cable Z makes sense for VD.

For I2R heating losses then R, of course!

Edit: @Julie. is probably the best one to ask for this!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Rockingit

Mentor
Arms
Supporter
~
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
r, x, & z - cable calcs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
Rockingit,
Last reply from
pc1966,
Replies
2
Views
1,496

Advert